David Rann

I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
 
I'm guessing you can't get RCBO's for whatever board you have already installed, can't see any problem but what are you going to do with the spare ways? , might they get used for something else in the future? and take the total load up past the 40 amp MCB?
 
That's on whoever installs after I presume. And I will put dedicated shower board. Someone suggested that I could have current issues down the neutral?
 
Hi - if I understand correctly you plan to have one shower per phase to spread the load. This means you will need L and N for each shower (i.e. each 10mm L needs its own 10mm N).
 
Hi - if I understand correctly you plan to have one shower per phase to spread the load. This means you will need L and N for each shower (i.e. each 10mm L needs its own 10mm N).
The triple-pole is a submain to another board for the showers.
 
I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
Yes, I’m thinking 16mm2.
 
Sorry I'm confused why would you need shower priority contactors? And are you saying you can't use a sub board?
 
Sorry I'm confused why would you need shower priority contactors? And are you saying you can't use a sub board?

You might not need to use them. Was just asking as curious. I have no knowledge of the type of installation, type of use, existing capacity etc.
 