I've been asked to price 3 X 7kw showers. There is a three phase board about 40 meters away. Can anyone see an issue with 40 amp three phase MCB with 10mm four core swa to a sub board then 3 X 32 amp rcbos for each individual shower.

Cheers
 
I'm guessing you can't get RCBO's for whatever board you have already installed, can't see any problem but what are you going to do with the spare ways? , might they get used for something else in the future? and take the total load up past the 40 amp MCB?
 
Hi - if I understand correctly you plan to have one shower per phase to spread the load. This means you will need L and N for each shower (i.e. each 10mm L needs its own 10mm N).
The triple-pole is a submain to another board for the showers.
 
Sorry I'm confused why would you need shower priority contactors? And are you saying you can't use a sub board?

You might not need to use them. Was just asking as curious. I have no knowledge of the type of installation, type of use, existing capacity etc.
 
What is a "shower priority contactor"?

Pre made units that can limit the amount of current drawn by only letting one shower be energised at a time.

For clarity, I'm not saying one needs to be used, but was asking if one was being used as I've never fitted one and would be interested if one was.
 

Reply to 3 X single phase showers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
828
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello all Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to...
Replies
5
Views
877
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock