Search the forum,

Discuss 3 X single phase showers in the UK Electrical Forum area at ElectriciansForums.net

Picking up the big hint from @westward10 - I had a go at a phasor diagram. If phase 1 shower is on, I get 30A (say) on the distribution circuit N. If phase 1,2 and 3 showers are all on then I get 0A on N, as they all cancel out. No big surprise as it's a balanced 3 phase load at that point. So what about when 2 showers are on? Hint - I was wrong before in #14 - it's my brain that's been flogged :) .


I give up Wilko. Do tell
 
Okay just been speaking to some that said even in the worst case scenario on an unbalanced system the neutral current will not exceed the highest of the phase. So if it's a 30 amp circuit then the maxmima neutral current is 30amp.

So many different responses and its clear I'm not the only one confused on this.

Cheers
 
Okay just been speaking to some that said even in the worst case scenario on an unbalanced system the neutral current will not exceed the highest of the phase. So if it's a 30 amp circuit then the maxmima neutral current is 30amp.

So many different responses and its clear I'm not the only one confused on this.

Cheers

This rings a bell, but honestly it's not a calculation I have performed many times since originally learning it. Makes more sense to me than the neutral current being the pure sum of the line currents.

I'd honestly have to dig out the books to draw the diagram properly but it shouldn't be too complex as the resistive loads should be considered in phase, i.e no lag or lead angles to adjust for ? Am I right ?
 
A shower passes a current of Iphase.

There are 3 phase currents I1, I2 and I3

Taking I1 as reference at 0deg, the I2 is =120 phase angle and I3 is 240deg (or -120deg)

Assume two showers on using I2 and I3, then In is I2 + I3 =

Iphase(cos120 +jsin120) + Iphase (cos-120 +jsin-120) =

Iphase (-0.5 + j0.58) + Iphase(-0.5 -j0.58)=

Ip (-0.5 + j0.58 -0.5 -j0.58) = -Iphase = -7000/240.

If you now add in a switched on I1 fed shower In = I1 + I2 + I3 =

Iphase-Iphase = 0

So, one shower magnitude of In = 7000/240A

Two showers magnitude of In = 7000/240A (but in anti-phase to the current the third off shower would pass).

Three showers In = 0A

Thus In is 7000/240 A for one or two showers or 0A fro three showers.

No need for N csa to be larger than line csa.
 
Last edited:
A shower passes a current of Iphase.

There are 3 phase currents I1, I2 and I3

Taking I1 as reference at 0deg, the I2 is =120 phase angle and I3 is 240deg (or -120deg)

Assume two showers on using I2 and I3, then In is I2 + I3 =

Iphase(cos120 +jsin120) + Iphase (cos-120 +jsin-120) =

Iphase (-0.5 + j0.58) + Iphase(-0.5 -j0.58)=

Ip (-0.5 + j0.58 -0.5 -j0.58) = -Iphase = -7000/240.

If you now add in a switched on I1 fed shower In = I1 + I2 + I3 =

Iphase-Iphase = 0


Huh?
 
upload_2018-10-8_22-9-31.png
 
The question is Marconi what will the neutral current be with two 30A loads across two phases but no load in the third phase. People are stating double the line current at 60A, this is not correct.

The magnitude of In will be 30A for one shower on, 30A for two showers on and 0A for three showers on.
 

Reply to 3 X single phase showers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
890
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello all Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to...
Replies
5
Views
901

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock