OP
- Reaction score
- 19
Picking up the big hint from @westward10 - I had a go at a phasor diagram. If phase 1 shower is on, I get 30A (say) on the distribution circuit N. If phase 1,2 and 3 showers are all on then I get 0A on N, as they all cancel out. No big surprise as it's a balanced 3 phase load at that point. So what about when 2 showers are on? Hint - I was wrong before in #14 - it's my brain that's been flogged .
I give up Wilko. Do tell