Anyone know if there is a reg in regards to supply going in to the top of a rotary isolator. We are changing the isolators over for ac units, long story short they won't reach the top terminals now, so feed can only go in bottom. Just a 2.5mm 3 core swa.
Cheers
I can’t see a problem, check that your not going against manufacturers instructions.
If it is not clear what the supply side is, then maybe a couple of labels over the terminal screw saying feed and load would be a nice touch to help the unwary.
Hi, yeah. That's what I thought. Just having a debate, if its correct. We are labelling the terminals. Nothing on instructions. Just wanted to know it works same, and not breaking regs
It works the same, it is a physical switch, opening a pair of contacts.
The only issue may be terminal identification
I’m pretty sure you can enter an enclosure any angle you like as long as your glands etc are installed properly, in fact, if the isolators external I would always try to avoid a top entry due to it maybe preventing unwanted leaks in the future
what's wrong with entering the enclosure from bottom and dressing the conductors into the top terminals of the isolator.
Reply to 32 amp rotary isolator in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
14K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...