We seem to be going round in circles, because we don't know your motivation in asking the question and hence what parameters you are aiming to specify. Do you have equipment that you want to operate in the UK that expects such a supply? Or do you want to apply BS7671 to an installation outside the UK with this supply configuration? Or is it purely an academic question?

The UK LV electrical supply is standardised as 230/400 with one leg of single phase supplies at or near ground potential, for general applications. For specific purposes, you can use whatever voltage and configuration is necessary, but not for the general wiring of buildings. The specification of the supply delivered to the consumer's terminals falls outside the scope of BS7671, governed instead by the ESQCR.

Portable appliances are also outside the scope of BS7671 and must achieve pan-EU compatibility in order to be CE-marked and hence permissible to sell. As per posts 19 & 29, a portable appliance has double-pole isolation inherent when unplugged, so does not require special provisions for compatibility with supplies of unknown polarity.
 
We seem to be going round in circles, because we don't know your motivation in asking the question and hence what parameters you are aiming to specify.

Ive asked what parameters I am interested in. Mainly if the IEC or BS allows such a system for domestic use and what special conditions need to be taken if any.

Do you have equipment that you want to operate in the UK that expects such a supply? Or do you want to apply BS7671 to an installation outside the UK with this supply configuration? Or is it purely an academic question?

Applying BS7671 to an installation outside the UK with such a configuration.


The UK LV electrical supply is standardised as 230/400 with one leg of single phase supplies at or near ground potential, for general applications. For specific purposes, you can use whatever voltage and configuration is necessary, but not for the general wiring of buildings.

What rules force 230 L-N for a building or domestic supply?


The specification of the supply delivered to the consumer's terminals falls outside the scope of BS7671, governed instead by the ESQCR.

Correct, but when a DNO provides 133/230Y TN-S as a supply, how can that be applied within the regs to a building?


Portable appliances are also outside the scope of BS7671 and must achieve pan-EU compatibility in order to be CE-marked and hence permissible to sell. As per posts 19 & 29, a portable appliance has double-pole isolation inherent when unplugged, so does not require special provisions for compatibility with supplies of unknown polarity.


I understand this part :) BTW, I think its the socket design that allows Schuko plugs in table lamps. The ones Ive seen appear to have a guard so the threads can not be touched when energized.
 
FFS just answer the question as to your location or do the mods need to look at your IP address?

Its not that difficult question is it?


Why does it matter? I am using IEC60364 with electricity obeying the same laws of physics regardless where that job will take place. Location will not answer my questions as to what a code or reg itself requires.
 
Last edited by a moderator:
Why does it matter? I am using IEC60364 with electricity obeying the same laws of physics regardless where that job will take place. Location will not answer my questions as to what a code or reg itself requires.

Very simply because when posters with hold facts, you start wondering what the F is going on..... why would concealing your location really matter?
 
Very simply because when posters with hold facts, you start wondering what the F is going on..... why would concealing your location really matter?


No, I think you simply dont know the answer. Sometimes people will shift the subject to avoid what they can not answer. Its either a simple yes or no with a code reference number. I have a good guess what will happen when I give a location: "check the local codes applicable to your country, they will have the answer your looking for" I this scenario its IEC60364 which BS7671 is closely modeled by.


FWIW when others post on forums like Mike Holt's asking about NFPA70 they are given responses around NFPA70 even if their location is Saudi Arabia or Brazil. Often over seas jobs require them asking such questions so no one asks to begin with.
 
But the regulations change according to location,

Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.
 
Last edited by a moderator:
Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.
Part p is an building reg, nothing to do with IET.
 
Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.

You cannot fulfill the requirements of part P with an installation designed to any regs other than bs7671
 
Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?

It is possible to design and construct an installation which uses such a supply in accordance with bs7671. However bs7671 is not law and so compliance with it cannot be described as legal. The law which governs electricity supplies in the uk is the electricity supply quality and continuity regulations (esqcr) which may prohibit such a supply from being provided to a customer.

Under bs7671 you would need to break all conductors which are not referenced to earth at substantially the same time, so yes you would need to provide double pole switching for light fittings.

Further to this you cannot use bs1363 plugs and sockets on such a supply as they are fused in one pole only, as a result the ring final circuit would not be useable. You would need to use a plug and socket system which is not fused or polarised, you may be able to use bs546 plugs and sockets for this.
 

Reply to 3x230 in the Talk Electrician area at ElectriciansForums.net

Similar threads

  • Locked
Thread closed.
2 3 4 5 6 7 8
Replies
110
Views
4K
  • Question
Can you do a sketch of the wires and their connections but @littlespark is probably correct.
Replies
4
Views
621

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top