• Thread starter Gardner
  • Start date
  • Replies 75
  • Views 6K

Currently reading:
3x230

Discuss 3x230 in the Electricians' Talk area at ElectriciansForums.net

We seem to be going round in circles, because we don't know your motivation in asking the question and hence what parameters you are aiming to specify. Do you have equipment that you want to operate in the UK that expects such a supply? Or do you want to apply BS7671 to an installation outside the UK with this supply configuration? Or is it purely an academic question?

The UK LV electrical supply is standardised as 230/400 with one leg of single phase supplies at or near ground potential, for general applications. For specific purposes, you can use whatever voltage and configuration is necessary, but not for the general wiring of buildings. The specification of the supply delivered to the consumer's terminals falls outside the scope of BS7671, governed instead by the ESQCR.

Portable appliances are also outside the scope of BS7671 and must achieve pan-EU compatibility in order to be CE-marked and hence permissible to sell. As per posts 19 & 29, a portable appliance has double-pole isolation inherent when unplugged, so does not require special provisions for compatibility with supplies of unknown polarity.
 
We seem to be going round in circles, because we don't know your motivation in asking the question and hence what parameters you are aiming to specify.

Ive asked what parameters I am interested in. Mainly if the IEC or BS allows such a system for domestic use and what special conditions need to be taken if any.

Do you have equipment that you want to operate in the UK that expects such a supply? Or do you want to apply BS7671 to an installation outside the UK with this supply configuration? Or is it purely an academic question?

Applying BS7671 to an installation outside the UK with such a configuration.


The UK LV electrical supply is standardised as 230/400 with one leg of single phase supplies at or near ground potential, for general applications. For specific purposes, you can use whatever voltage and configuration is necessary, but not for the general wiring of buildings.

What rules force 230 L-N for a building or domestic supply?


The specification of the supply delivered to the consumer's terminals falls outside the scope of BS7671, governed instead by the ESQCR.

Correct, but when a DNO provides 133/230Y TN-S as a supply, how can that be applied within the regs to a building?


Portable appliances are also outside the scope of BS7671 and must achieve pan-EU compatibility in order to be CE-marked and hence permissible to sell. As per posts 19 & 29, a portable appliance has double-pole isolation inherent when unplugged, so does not require special provisions for compatibility with supplies of unknown polarity.


I understand this part :) BTW, I think its the socket design that allows Schuko plugs in table lamps. The ones Ive seen appear to have a guard so the threads can not be touched when energized.
 
FFS just answer the question as to your location or do the mods need to look at your IP address?

Its not that difficult question is it?


Why does it matter? I am using IEC60364 with electricity obeying the same laws of physics regardless where that job will take place. Location will not answer my questions as to what a code or reg itself requires.
 
Last edited by a moderator:
Why does it matter? I am using IEC60364 with electricity obeying the same laws of physics regardless where that job will take place. Location will not answer my questions as to what a code or reg itself requires.

Very simply because when posters with hold facts, you start wondering what the F is going on..... why would concealing your location really matter?
 
Very simply because when posters with hold facts, you start wondering what the F is going on..... why would concealing your location really matter?


No, I think you simply dont know the answer. Sometimes people will shift the subject to avoid what they can not answer. Its either a simple yes or no with a code reference number. I have a good guess what will happen when I give a location: "check the local codes applicable to your country, they will have the answer your looking for" I this scenario its IEC60364 which BS7671 is closely modeled by.


FWIW when others post on forums like Mike Holt's asking about NFPA70 they are given responses around NFPA70 even if their location is Saudi Arabia or Brazil. Often over seas jobs require them asking such questions so no one asks to begin with.
 
But the regulations change according to location,

Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.
 
Last edited by a moderator:
Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.
Part p is an building reg, nothing to do with IET.
 
Thats not even a valid answer. I know of many instances where foreign codes are applied in another country such as for example NFPA70 in US military installations inside the Middle East. Second many poor countries use the raw IEC60364 with little change. Third its possible to wire any building in the UK with say the German or French regs provided part P can be proven as fulfilled.

You cannot fulfill the requirements of part P with an installation designed to any regs other than bs7671
 
Is such a system (230 volt L-L) legal under BS7671 or IEC 60364? Do I need double pole switches for light fittings?

It is possible to design and construct an installation which uses such a supply in accordance with bs7671. However bs7671 is not law and so compliance with it cannot be described as legal. The law which governs electricity supplies in the uk is the electricity supply quality and continuity regulations (esqcr) which may prohibit such a supply from being provided to a customer.

Under bs7671 you would need to break all conductors which are not referenced to earth at substantially the same time, so yes you would need to provide double pole switching for light fittings.

Further to this you cannot use bs1363 plugs and sockets on such a supply as they are fused in one pole only, as a result the ring final circuit would not be useable. You would need to use a plug and socket system which is not fused or polarised, you may be able to use bs546 plugs and sockets for this.
 
It is possible to design and construct an installation which uses such a supply in accordance with bs7671. However bs7671 is not law and so compliance with it cannot be described as legal. The law which governs electricity supplies in the uk is the electricity supply quality and continuity regulations (esqcr) which may prohibit such a supply from being provided to a customer.

Thanks :)

Under bs7671 you would need to break all conductors which are not referenced to earth at substantially the same time, so yes you would need to provide double pole switching for light fittings.

Got it. All MCBs are 2 and 3p. What part of the regs require 2p switching for light fittings? Not saying it does not exist but just want to have a reg reference.

Further to this you cannot use bs1363 plugs and sockets on such a supply as they are fused in one pole only, as a result the ring final circuit would not be useable. You would need to use a plug and socket system which is not fused or polarised, you may be able to use bs546 plugs and sockets for this.

Schuko plugs will be used with 16 amp MCBs. No rings either.
 
Exactly my point. I could wire a building with German regs, nothing holds me to BS7671.

In Germany yes you can, however if you are in England then you abide by our rules.

As far as England goes:
The registration bodies would not accept it.
LABC would not accept it.
Insurance companies would not accept it.
The HSE would not accept it in an investigation if an incident occurred.
A Judge would not accept it if you were put on trial as a result of said incident.
 
In Germany yes you can, however if you are in England then you abide by our rules.

As far as England goes:
The registration bodies would not accept it.
LABC would not accept it.
Insurance companies would not accept it.
The HSE would not accept it in an investigation if an incident occurred.
A Judge would not accept it if you were put on trial as a result of said incident.

Fair enough. But to be honest, I remember on another forum saying BS7671 should be publicly disclosed for free because its law with posters saying its not law since part P does not mandate it... A bit confused.

But anyways... if the sockets at Bayonet, do I still need DP switching?
 
But its not mandated, is it? Should is not shall.

That is a technical point which would take some expensive legal professionals to argue over.

I think the general idea is that nobody would be so downright stupid as to work to non-uk regulations in general installations in the uk! It would make you uncompetitive in terms of price and get you a terrible reputation when all of your customers find out that you have not worked to uk regulations.
 
That is a technical point which would take some expensive legal professionals to argue over.

I think the general idea is that nobody would be so downright stupid as to work to non-uk regulations in general installations in the uk! It would make you uncompetitive in terms of price and get you a terrible reputation when all of your customers find out that you have not worked to uk regulations.

Makes sense.

For those who dont believe 138/240Y is not a real DNO supply voltage here is the tag on a transformer which is used in a 3 phase bank to provide a 240 volt 3 phase L-L supply:
 

Attachments

  • poletransformertag.jpg
    135.8 KB · Views: 33
Fair enough. But to be honest, I remember on another forum saying BS7671 should be publicly disclosed for free because its law with posters saying its not law since part P does not mandate it... A bit confused.

But anyways... if the sockets at Bayonet, do I still need DP switching?

BS7671 is not law but it is referenced in law. Part P is only concerned with domestic installations.

The type of lampholder is irrelevant to the switching requirement, the requirement is that all line conductors (ie. all conductors not connected to earth at source) be broken.

The question of lampholders is a seperate issue. The regulations require that the outer contact of ES lampholders be connected to neutral, therefore you cannot use a two phase supply with an ES lampholder. You can use pretty much every other type of lampholder including BC, GU10, GX, GY etc etc
 
BS7671 is not law but it is referenced in law. Part P is only concerned with domestic installations.

So the option is indeed their to wire something to other regs?

The type of lampholder is irrelevant to the switching requirement, the requirement is that all line conductors (ie. all conductors not connected to earth at source) be broken.

Is this mandated by any particular reg? I just dont know how I would go about 2 way switches.


The question of lampholders is a seperate issue. The regulations require that the outer contact of ES lampholders be connected to neutral, therefore you cannot use a two phase supply with an ES lampholder. You can use pretty much every other type of lampholder including BC, GU10, GX, GY etc etc

Is BC bayonet? GU10 is easy to get with LED. Easy route to take with LED.
 
So the option is indeed their to wire something to other regs?



Is this mandated by any particular reg? I just dont know how I would go about 2 way switches.




Is BC bayonet? GU10 is easy to get with LED. Easy route to take with LED.

Only as far as bs7671 being non-statutory is concerned. Your insurance would likely be void and you would open yourself up to a heck of a liability should anything go wrong!

I don't have a regs book to hand, but the section called isolation and switching would be a good place to start. I assume you own a current copy of bs7671 if you are designing to it?

BC is bayonet cap yes. LED gu10 is the cheap and easy option yes but are not great when compared to a fitting designed and built using an LED source from the outset.
 
Only as far as bs7671 being non-statutory is concerned. Your insurance would likely be void and you would open yourself up to a heck of a liability should anything go wrong!

I don't have a regs book to hand, but the section called isolation and switching would be a good place to start. I assume you own a current copy of bs7671 if you are designing to it?

BC is bayonet cap yes. LED gu10 is the cheap and easy option yes but are not great when compared to a fitting designed and built using an LED source from the outset.


Sounds great, I will take a look at switching and isolation! :)

EFLI and disconnect times are still 0.4 seconds for TN?
 
So as I understand it now, you are designing an installation outside the UK, where UK building regs do not apply, where the supply is not of the type provided by UK DNOs, but you wish to comply as far as possible with BS7671 or use the standard as the design framework. A lot of head scratching could have been avoided if this had been explained in the OP, as this is a forum primarily for UK electricians working to UK regs in the UK.

You substitute Schuko and radials for BS1363 and rings, to avoid the problems mentioned above, and provide DP OCP and isolation throughout. And then we get to 2-way light switching and I am going to hide behind a pile of DP relays!
 

Reply to 3x230 in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top