Discuss 411.8.3 Requirement for Fault Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Where fault protection is provided by an RCD, the product of the rated residual operating current (IΔn) in amperes
and the earth fault loop impedance in ohms shall not exceed 50 V.
"Where fault protection is provided by an RCD, the product of the rated residual operating current (IΔn) in amperes and the earth fault loop impedance in ohms shall not exceed 50 V".
Reply to 411.8.3 Requirement for Fault Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
I would appreciate some opinions on the following situation... I have been asked to comment on an EICR for a local community resource (church hall...
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...