Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
I totally agree. I often find sparks stating 4mm radials on a 32 OCPD are the best thing since sliced bread but as you say the limitations are often over looked and they don't want to hear it when you point them out.
 
True, I certainly wouldn't install it like this either. But as its already there, I didn't flag it as an issue with the homeowners. There were several other more pressing issues, like downlights covered in insulation and running 50w halogens!
 
Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
I would be bothered about it yes.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

kingeri

Arms
-
Joined
Location
Yorkshire

Thread Information

Title
4mm 32a Radial In Trunking
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
kingeri,
Last reply from
7029 dave,
Replies
9
Views
6,655

Advert

Back
Top