kingeri

-
Esteemed
Arms
Reaction score
1,345
Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
I totally agree. I often find sparks stating 4mm radials on a 32 OCPD are the best thing since sliced bread but as you say the limitations are often over looked and they don't want to hear it when you point them out.
 
True, I certainly wouldn't install it like this either. But as its already there, I didn't flag it as an issue with the homeowners. There were several other more pressing issues, like downlights covered in insulation and running 50w halogens!
 
Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
I would be bothered about it yes.
 

Reply to 4mm 32a Radial In Trunking in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Guys needvadvice please I was asked to carry out an annual inspction of a DB recently There are 12 in number radial circuits suppling sockets...
Replies
3
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Morning all, I‘d really appreciate some advice - not a kick in the pants please - from those more knowledgeable than me! My new kitchen and...
Replies
37
Views
6K
For a change its nice to have a clean slate to work to. Client wants their garage rewired (and boy does it need it!) so they can have the...
Replies
12
Views
3K
Hi all, working with a spark today, basically dodgy wiring in kitchen junction boxes everywhere, all ripped out, now all we’re doing is a new 6mm...
Replies
22
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock