Hi, just finished a partial rewire at my sisters house and when testing the two lighting circuits (up&down) the 6AMCB trips for both circuits individually, I thought the MCBs might just be sensitive to the test but the smoke alarm circuit also 6A is fine when testing, R1+R2 and IR test all fine just the Loop test causing issues, any ideas??

Thanks Lewis
 
Answer to all three above, the circuits have rcd protection, was a three prob test, megger 1552 tester and that is what I did in the end add r1+r2 to Ze just the fact it tripped two off the 6a mcbs and not all three is what threw me off.
 
Hi - Do I understand correctly (?) you are trying to measure Zs on a circuit using the low current test (due to RCD presence) and the OCPD trips.
 