Discuss 6mm or 10mm for cooker? in the UK Electrical Forum area at ElectriciansForums.net
HappyHippyDad
I don't think I've ever come across a cooker that needs 10mm but I may err on the side of caution with this one.
Rangemaster Leckford deluxe 110cm induction range cooker.
14.8kW, states required a 45A supply.
No info on cable size.
With diversity a 6mm will be ok. Plus ref method C gives a ccc of 47A for 6mm.
But... it's close. Would you use 10mm?
We had a Rangemaster, with gas hobs. Manufacturer stated 40A supply. We had it connected by one of their ’engineers’, cos they would take away the old cooker, a Curry’s free deal thing.
He said we were lucky, we had a 40A supply, otherwise he couldn’t connect it up.
Clamped it some later going full guns (two ovens and grill). Never pulled more than 14A.
Think it says in app 15, that 6mm is good for radial cooker appliances up to 15kW. But I’d go for 10mm, not much of a price difference.
We have a rangemaster that stated 40a mcb. It's wired in 6mm and on a 32a mcb. Never did get round to changing it but causes absolutely no problems.
6mm not 10mm but 6mm think of diversity
Cheers guys,
I got through rangemaster who stated a 10mm was required. They didn't really give a proper response as to why, but in reality I think a 10mm for this type of cooker is best as any variance in reference type would mean the 6mm is not adequate.
Didn't have enough 10mm on the van so back tomorrow!
10mmis just a waste of copper. think of the polar beara and install 6mm.
The manufacturer obviously hasn't just taken the 14.8kW and based their current rating on that, so there may be a good reason they state 45A supply.
Personally I highly doubt a supply over 32A is actually required but without seeing the detailed specs for the appliance I won't commit to that.
The only time I've known a domestic cooker need more than 32A was a massive dual fuel thing with gas hobs and electric ovens made by wolf. The manufacturers said it needed 50A which was based on the total power rating, so we installed 10mm but we could only get a 45A MCB so that's what we fitted.
It was absolutely fine in normal use, but when the customer put all of the ovens (I've got a feeling there were 4) into self cleaning mode at the same time it overloaded and tripped the 45A mcb.
The soloution was obviously to advise the customer not to clean all of the ovens at once.
I would put it on 6mm and have done and if rangemaster refused to connect it up would do it myself, it could never actually run 15kw no way on earth, bit of 10mm never hurt I suppose but if it says it in the onsite guide it's good enough for me
Is the refrence method really C? Or is that the one that allows you to skimp? Ridiculous not to run a 10mm t&e to any new cooker or shower in my opinion, i use very little 6mm t&e these days.
I've noticed that over the last couple of years or so larger domestic cookers or ranges being available and purchased by customers either on-line or from the likes of Currys, John Lewis etc and likewise five ring instead of four ring hobs. I wonder if they're setting up cafes in their homes. Anyway, bigger appliances, bigger currents. I tend to check and calculate first and not just rely on 6mm as the go to norm anymore.
Think he's recommending 35mm to you T......
I bought new Range-master estate 90 dual cooker, I have got 6mm coming from the fuse for the old cooker. The cooker requires a 10m for connection. Now do i have to take a 1om from fuse box to the cooker socket in the kitchen. Please advise.
10mm for the entirety of the circuit, time to get a spark in
Yep from the consumer unit (fuse) all the way to the isolation point and then on to the cooker connector plate…..have you thought about a lower power oven? 😬
So 10m from the fuse box to the main cooker socket replacing the 6m. That would need an outlet box to. Please advise on that. This cooker do not have any cables attached to it, you have to make it from the 10m cable to attach to the cooker socket. Pls correct me if i am wrong. RANGEMASTER DUAL COOKER ESTATE 90.
Reply to 6mm or 10mm for cooker? in the UK Electrical Forum area at ElectriciansForums.net
Hello Guys Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven. I've looked at...
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Have had an estimate accepted for a CU change in a 1980s bungalow. I based the estimate mainly on an EICR which was carried out on the property...
I'm reading a thread at the moment about a 9.8kW shower that has been installed on a 6mm cable. My natural instinct was to think that's wrong, it...
6K