SuperlecDirect - ElectriciansForums.net Electrical Suppliers
Discuss 6mm or 10mm for cooker? in the Electrical Forum area at ElectriciansForums.net
happyhippydad
I don't think I've ever come across a cooker that needs 10mm but I may err on the side of caution with this one.
Rangemaster Leckford deluxe 110cm induction range cooker.
14.8kW, states required a 45A supply.
No info on cable size.
With diversity a 6mm will be ok. Plus ref method C gives a ccc of 47A for 6mm.
But... it's close. Would you use 10mm?
CK Tools :) The professionals choice when it comes to Electrical Tools
Midwest
We had a Rangemaster, with gas hobs. Manufacturer stated 40A supply. We had it connected by one of their ’engineers’, cos they would take away the old cooker, a Curry’s free deal thing.
He said we were lucky, we had a 40A supply, otherwise he couldn’t connect it up.
Clamped it some later going full guns (two ovens and grill). Never pulled more than 14A.
Think it says in app 15, that 6mm is good for radial cooker appliances up to 15kW. But I’d go for 10mm, not much of a price difference.
Matthewd29
We have a rangemaster that stated 40a mcb. It's wired in 6mm and on a 32a mcb. Never did get round to changing it but causes absolutely no problems.
Pete999
6mm not 10mm but 6mm think of diversity
happyhippydad
  • #6
Cheers guys,
I got through rangemaster who stated a 10mm was required. They didn't really give a proper response as to why, but in reality I think a 10mm for this type of cooker is best as any variance in reference type would mean the 6mm is not adequate.
Didn't have enough 10mm on the van so back tomorrow!
davesparks
Mentor
The manufacturer obviously hasn't just taken the 14.8kW and based their current rating on that, so there may be a good reason they state 45A supply.
Personally I highly doubt a supply over 32A is actually required but without seeing the detailed specs for the appliance I won't commit to that.
The only time I've known a domestic cooker need more than 32A was a massive dual fuel thing with gas hobs and electric ovens made by wolf. The manufacturers said it needed 50A which was based on the total power rating, so we installed 10mm but we could only get a 45A MCB so that's what we fitted.
It was absolutely fine in normal use, but when the customer put all of the ovens (I've got a feeling there were 4) into self cleaning mode at the same time it overloaded and tripped the 45A mcb.
The soloution was obviously to advise the customer not to clean all of the ovens at once.
robd
I would put it on 6mm and have done and if rangemaster refused to connect it up would do it myself, it could never actually run 15kw no way on earth, bit of 10mm never hurt I suppose but if it says it in the onsite guide it's good enough for me
bigspark17
Is the refrence method really C? Or is that the one that allows you to skimp? Ridiculous not to run a 10mm t&e to any new cooker or shower in my opinion, i use very little 6mm t&e these days.
JOURNEYMAN
I've noticed that over the last couple of years or so larger domestic cookers or ranges being available and purchased by customers either on-line or from the likes of Currys, John Lewis etc and likewise five ring instead of four ring hobs. I wonder if they're setting up cafes in their homes. Anyway, bigger appliances, bigger currents. I tend to check and calculate first and not just rely on 6mm as the go to norm anymore.
ipf
Mentor
10mmis just a waste of copper. think of the polar beara and install 6mm.
Think he's recommending 35mm to you T......
Reply to 6mm or 10mm for cooker? in the Electrical Forum area at ElectriciansForums.net