But remember, we only work to 230v, most supplies I come across are still nearer 240...…...I'll bet them Brexit burgers aren't too bothered about our small discrepancies, though.
Indeed, but 240 is still within the permitted voltage range of a 230V nominal supply, so you'd like to think that equipment designed to operate on a 230V supply, with design calculations using the 230V nominal figures, would be perfectly capable of safe operation at the worst case scenario within the permitted voltage range.
The actual supply voltage should not invalidate calcs carried out based on 230V provided it is within the range permitted by ESQR.
 
Perhaps 10mm Is the safer option to cover future installs with bigger loads ... or indicative of a previous heavier rated shower?
 
Indeed, but 240 is still within the permitted voltage range of a 230V nominal supply, so you'd like to think that equipment designed to operate on a 230V supply, with design calculations using the 230V nominal figures, would be perfectly capable of safe operation at the worst case scenario within the permitted voltage range.
The actual supply voltage should not invalidate calcs carried out based on 230V provided it is within the range permitted by ESQR.
Nowt to do with it, mate. Just a point in replying to #16.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Why do we fit a 10mm cable for showers?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
ipf,
Replies
22
Views
7,740

Advert