But remember, we only work to 230v, most supplies I come across are still nearer 240...…...I'll bet them Brexit burgers aren't too bothered about our small discrepancies, though.
Indeed, but 240 is still within the permitted voltage range of a 230V nominal supply, so you'd like to think that equipment designed to operate on a 230V supply, with design calculations using the 230V nominal figures, would be perfectly capable of safe operation at the worst case scenario within the permitted voltage range.
The actual supply voltage should not invalidate calcs carried out based on 230V provided it is within the range permitted by ESQR.
 
Perhaps 10mm Is the safer option to cover future installs with bigger loads ... or indicative of a previous heavier rated shower?
 
Indeed, but 240 is still within the permitted voltage range of a 230V nominal supply, so you'd like to think that equipment designed to operate on a 230V supply, with design calculations using the 230V nominal figures, would be perfectly capable of safe operation at the worst case scenario within the permitted voltage range.
The actual supply voltage should not invalidate calcs carried out based on 230V provided it is within the range permitted by ESQR.
Nowt to do with it, mate. Just a point in replying to #16.
 

Reply to Why do we fit a 10mm cable for showers? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
348
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
425
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
736
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock