Have had an estimate accepted for a CU change in a 1980s bungalow. I based the estimate mainly on an EICR which was carried out on the property by another spark last summer, plus I had a quick look at the existing board, meter, and bonding.

The EICR has all circuits listed as ref method C, but I suspect there's a good chance it'll actually be method 101 - I expect cables for all circuits to be under insulation in the loft. Ok, no problem for the lighting circuits on 6A breakers, but the CCC of the 3 ring finals (2.5mm = 17A) and 2 cooker circuits (6mm = 27A) would be too low for 32A breakers.

Assuming that the cables are in good condition, no signs of thermal damage, what do you guys and girls do in this situation? Derating the breakers is one option, but could lead to nuisance tripping, at least for the kitchen circuits. Putting the cables in conduit is another, but it's a lot of itchy work up there that I'd like to avoid if possible, and will add a lot to the price.
 
Any option for 25A RCBO for your chosen board? Would safely do both circuits.

But try to check the loft cables first, as if method 100 then should be fine on the usual 32A.
 
Any option for 25A RCBO for your chosen board? Would safely do both circuits.

But try to check the loft cables first, as if method 100 then should be fine on the usual 32A.
Thanks @pc1966 . Yes, it'll be a Hager RCBO board so 25A are available.

I had considered 25A for the rings, based on the old ratio of cable rating => 2/3rds of the breaker rating. Anecdotally, this was changed to cable rating => 20A, to allow 32A breakers to protect rings installed to the same installation methods as those protected by 30A fuses.
 
Last edited:

Reply to Bungalow board change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
Afternoon all. I’m doing a dorma / loft extension all circuits for that extension are new . I’m going to upgrade the consumer unit also to...
Replies
1
Views
944
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock