I had an interesting little job this morning.
Three sockets in an extension were not working and haven't worked for quite some time (years).
It has perplexed a series of electricians. The last one was a friend of mine and invited me to have a look.

Flat roof above. Tiled floor. Ceiling had completely collapsed at some point and been repaired leading to suspicions of cable damage.
All 3 sockets had two cables running up towards ceiling.
No end-to-end continuity at the sockets.

The CU end of things:
1711981720443.png


My friend had already done some testing that he didn't find conclusive, so I decided to start again from first principles.
-Both main switches off.
-Take one of the non-working sockets completely off.
-Test both RFC's in top board, and both had perfect end-to-end continuity for all conductors.
-Conclude the circuit is nothing to do with two sockets circuits in top CU (unless the whole lot is a long spur which seemed unlikely)
-Refit the socket

So I look at bottom CU which was once for storage heaters (property now has central heating).
One circuit had two conductors though they are of different ages.
A quick test, and I could pickup L-E continuity at all three sockets

1711982326265.png

Same applied with L-N

Checked end-to-end at board and 0/3
Checked fuse - all fine.

So at this point I have an open-circuit ring or radial, suspicion that one of the legs in the board is actually nothing to do with it, no obvious location the far end of the circuit is going to, and the glaring question as to why the sockets weren't showing signs of life.

IR test of the working leg L+N to E = 10M. Good enough.
Check there is power at incomer, there is.

Which can only really leave one thing:

1711982625033.png


Yep, main switch not working.

My suspicion is:
-the sockets have always been a radial and there are one or more point(s) at the end of the circuit. (There's a new looking en-suite in the next room.)
-they should never have been in a 30 amp fuse in the first place.
-maybe the contacts of the main switch were deliberately removed when the central heating was installed?!

Anyway, the long overdue board change can sort all this out one way or another.
 

Reply to Well that explains it then... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
542
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
755
Helping out a friend and a CU change is really the best option as sockets in kitchen and downstairs room not on RCD protection. Now one of the WTF...
Replies
11
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock