while doing EICRs i often find this combination, if its clipped direct it dont worry me
however many times i have no idea how the cable is routed
im just wondering how others would code this?
 
I wouldn’t code it unless evidence of thermal damage, that’s if it wasn’t obvious that it was installed in a reference method lower than the Ib or Iz of the circuit
 
It would depend on what load is attached to it.

agreed, if the load is 34A for a fixed appliance the no problem. you can do the calcs. and see if the circuit is good for continued use.
 
Don't forget that there is a part of the certificate that is a disclaimer for cable concealed in the fabric of the building.
 
As long as there’s no risk of over current then no code.
 
Does it matter what load is attached? If there was no load whatsoever, so let's say a 6mm t+e directly into a spur but no load, protected by a 40a mcb but going through insulation. Would you code it?
 
Does it matter what load is attached? If there was no load whatsoever, so let's say a 6mm t+e directly into a spur but no load, protected by a 40a mcb but going through insulation. Would you code it?

Yes it does matter, if there is a fixed load not subject to overload faults then the cable may not require overload protection, so can be sized according to the load current rather than ocpd rating.

Assuming by spur you mean a fused spur then there is technically no problem because the load will be limited to 13A, though I may suggest that a lower rated mcb would be more appropriate.
 

Reply to 6mm T&E on 40 amp mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
754
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
607
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock