Discuss 7 core NYYJ cable to extend ring final circuit? in the UK Electrical Forum area at ElectriciansForums.net
Hi,
Extending a ring final circuit off a socket in the kitchen through the wall into the shed on the other side. I already have 7 core NYYJ 2.5mm cable and I was wondering if I could use that to go through the wall to a J/B then connect to singles in conduit which would add about 4 meters in total to the ring (2 meters there and back)
Do people use multi core cable to extend rings? Or is it always 2 x 3 core? Do they use multi core to go through walls? I liked the added protection of the cable.
If you have any suggestions that would be great help.
No reason why you cant use the 7 core, but as above, it would be a better job to use conduit and singles all the way into the kitchen socket.
As an aside have you actually verified the socket you are coming from is on a ring? Just because there are two cables don't assume, particularly if a kitchen fitter has altered/installed anything in the past.
You need to check the ccc of a 7-core cable as it may well fall below what is required for a ring final circuit.
2 core 2.5 mm Nyyj on eland cables web site is 27 amps in air.
7 core is 16 amps in air however the 7 core ccc rating is for 7 loaded cores, if your only using 2 cores (not counting the cpc core as it’s not carrying current) id imagine you can use the higher rated ccc.
I’d rather not have all the extra cores there to be honest , I wouldn’t use it.
Although, as part of a ring, four cores could be equally loaded by a concentration of load just to one side of the multicore-fed section. I am suspicious, without any data to back it up, that on paper it would not have sufficient CCC.
The cores must be rated at 20A if being used on a ring final circuit normally sized at 2.5 unless it is MI where 1.5 can be used however, plenty of ring finals have been installed over the years using 4-core MI which is not actually rated for 20A. Like SY, correction factors are applied to NYY J cables when the quantity of cores exceeds five.
Reply to 7 core NYYJ cable to extend ring final circuit? in the UK Electrical Forum area at ElectriciansForums.net
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...