A question regarding S7. Mobile Transportable Units. Would the main double pole Isolator of the mobile cabin and the Main isolator in the supplying panel behind adequate for mechanical isolation for maintenance without an additional isolator socket, if the cabin is connected between the two with plug and socket? They require it on plugs to be temporary. The supply is TT. I can't see a reg saying it must have an isolator socket also but often see them with this. A colleague is proposing not using an isolator socket to avoid having to wait for ordering one. If an isolator socket is not necessary it poses another question. As the socket on the transportable cabin must be male then this would require a female plug to be run from the board, which is an unusual set up, I've never seen. I know if it were a socket it would require a 32mA RCD prior, in the supplying board, so using an isolator socket would make it much more obvious. Logically I'd imagine this would need the same but can't find anything about this situation? Apparently there's a 32mA RCD in the cabin also but currently a 40 mA rcd on the board. Hopefully someone on here is knowledgeable about standard practice for this situation.
 
A question regarding S7. Mobile Transportable Units. Would the main double pole Isolator of the mobile cabin and the Main isolator in the supplying panel behind adequate for mechanical isolation for maintenance without an additional isolator socket, if the cabin is connected between the two with plug and socket? They require it on plugs to be temporary. The supply is TT. I can't see a reg saying it must have an isolator socket also but often see them with this. A colleague is proposing not using an isolator socket to avoid having to wait for ordering one. If an isolator socket is not necessary it poses another question. As the socket on the transportable cabin must be male then this would require a female plug to be run from the board, which is an unusual set up, I've never seen. I know if it were a socket it would require a 32mA RCD prior, in the supplying board, so using an isolator socket would make it much more obvious. Logically I'd imagine this would need the same but can't find anything about this situation? Apparently there's a 32mA RCD in the cabin also but currently a 40 mA rcd on the board. Hopefully someone on here is knowledgeable about standard practice for this situation.
I used to fit caravan hook up meter boxes. The ones we fit had a meter then a double pole rcbo as the isolator.
We used no rotary isolator.

A 60947 is a double pole isolator, a double pole rcbo is a double pole isolator.
If you can isolate both conductors it is isolated and therefore is an isolator.

The hookup boxes we used had female sockets. You don't want the supply end having the plug as that would be a suicide plug.
 

OFFICIAL SPONSORS

Back
Top