Looks like a stone bonker fraud or attempted fraud. Don’t think the 2006 Fraud Act applies in Scotland with you guys dealing with a lot of stuff under Common Law which covers most things fraudulent. I hope the builder is going to see the client right and the dodgy spark has carefully hidden his stash! Pigs might fly though given the current state of law enforcement.
 
Are those terminals showing signs of "Mutilation"
by a very Peed off electrician ?
Or just some one who has a Wood butchers screwdriver kit !

This is what wood butchering looks like.

Quite why anyone would drill this size of hole for a 1.5 mm twin and earth mystifies me. The imbecile who did this has made no attempt to seal the hole. Remember, this is a brand-new installation that someone has done an EICR on and rated as being 'satisfactory'.

IMG_20190807_090807.jpg
 
This is a one of five glands that were found to be loose inside and out. The top of the gland was barely hand-tight, and as is evidenced by the photo, the bottom half wasn't fully inserted in the entry hole.

20190807_095115.jpg
 
40 amp breaker fitted to a ring final circuit!

20190807_095108.jpg
 
Deep gashes in the L1 and L3 tails.

20190807_100125.jpg
 
The only clip securing the tails and main earth is that solitary T&E clip.

20190807_100222.jpg
 
This is a brand-new board. Words fail me.

20190807_100136.jpg
 
This is how the wiring looks when viewed from behind the board. All the cables have been taped together and left dangling.

20190807_100237.jpg
 
These SWAs were wrapped together with plastic cable ties and left dangling.

20190807_100228.jpg
 