Deep gashes in the L1 and L3 tails.

A Rather Obvious Forged EICR 20190807_100125 - EletriciansForums.net
 
The only clip securing the tails and main earth is that solitary T&E clip.

A Rather Obvious Forged EICR 20190807_100222 - EletriciansForums.net
 
This is a brand-new board. Words fail me.

A Rather Obvious Forged EICR 20190807_100136 - EletriciansForums.net
 
This is how the wiring looks when viewed from behind the board. All the cables have been taped together and left dangling.

A Rather Obvious Forged EICR 20190807_100237 - EletriciansForums.net
 
These SWAs were wrapped together with plastic cable ties and left dangling.

A Rather Obvious Forged EICR 20190807_100228 - EletriciansForums.net
 
I would say the block with the blue conductors at it looks like it shows signs of melting.

You are correct. I'm informed that prior to a 16mm SWA being installed to supply a sub-board for the office area, one of those twin and earths was acting as the supply cable! Apparently whoever installed the sub-board connected all the final circuits, but for reasons best known to himself, decided to spur the supply for the board from a ring final circuit elsewhere in the building. I don't know what he was thinking.
 
Why is there a smoke detector circuit on that type of installation unless it is a fire alarm,

There's a fire alarm panel, smoke alarms, call points and sounders present. I noticed that the panel is indicating a fault condition.

However, no certificate other than a MEIWC has been issued. Whoever did the work submitted a MEIWC to cover the design, installation and commissioning! There is no certification for the emergency lighting either.
 
Sounds like someone well and truly out of their depth.

That was my conclusion too. There is insufficient capacity in the main board. All the ways have been used. One of the breakers has three conductors. Two supply the main area lighting and emergency lighting. The other supplies one of the shuttered doors of which there are five in total. Another of the doors has been spurred direct from the ring final circuit.
 

Reply to A Rather Obvious Forged EICR in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock