These connections are for three shuttered doors!

IMG_20190807_090717.jpg


IMG_20190807_152117_1.jpg


IMG_20190807_153716.jpg

 
  • Like
Reactions: nicebutdim
40 amp breaker fitted to a ring final circuit!

20190807_095108.jpg
 
Deep gashes in the L1 and L3 tails.

20190807_100125.jpg
 
The only clip securing the tails and main earth is that solitary T&E clip.

20190807_100222.jpg
 
This is a brand-new board. Words fail me.

20190807_100136.jpg
 
Least they glanded each tail separately :D
 
  • Like
Reactions: stevethesparks
This is how the wiring looks when viewed from behind the board. All the cables have been taped together and left dangling.

20190807_100237.jpg
 
These SWAs were wrapped together with plastic cable ties and left dangling.

20190807_100228.jpg
 
Not knocking house bashers but this looks like one totally out of their depth.
 
It's a house basher all day long.
 
I would say the block with the blue conductors at it looks like it shows signs of melting.

You are correct. I'm informed that prior to a 16mm SWA being installed to supply a sub-board for the office area, one of those twin and earths was acting as the supply cable! Apparently whoever installed the sub-board connected all the final circuits, but for reasons best known to himself, decided to spur the supply for the board from a ring final circuit elsewhere in the building. I don't know what he was thinking.
 
  • Like
Reactions: westward10
Why is there a smoke detector circuit on that type of installation unless it is a fire alarm,

There's a fire alarm panel, smoke alarms, call points and sounders present. I noticed that the panel is indicating a fault condition.

However, no certificate other than a MEIWC has been issued. Whoever did the work submitted a MEIWC to cover the design, installation and commissioning! There is no certification for the emergency lighting either.
 
  • Like
Reactions: westward10
Sounds like someone well and truly out of their depth.
 
  • Like
Reactions: JK-Electrical
I would question if this was an electrician at all...

The person who did the work advertises himself as an electrician. However, I would advise him to quit the trade and seek alternative employment.
 
  • Like
Reactions: James
Sounds like someone well and truly out of their depth.

That was my conclusion too. There is insufficient capacity in the main board. All the ways have been used. One of the breakers has three conductors. Two supply the main area lighting and emergency lighting. The other supplies one of the shuttered doors of which there are five in total. Another of the doors has been spurred direct from the ring final circuit.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Glasgow
Website
http://www.jkelectricalservices.com
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
JK Electrical

Thread Information

Title
A Rather Obvious Forged EICR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
56

Advert

Thread statistics

Created
JK-Electrical,
Last reply from
magnoliafan89,
Replies
56
Views
8,065

Advert