Well I am rather happy to say that today we managed to sort this piece o crap out.
So we original went to this thing with the POV that it hadnt run in a while due to some fault nobody had fixed.
As it turns out there is no way in hell this thing had ever run properly in the condition it was in, Which is very probably when it was modified to be inverter driven.

The final list of faults (and I use that term loosely) is rather long, So we came away with the POV the guy who mod'd it was a flaming idiot who had no idea what he was doing!

Highlights of the problems include:

Burnt out Dis Board
Burnt out breaker
Incorrectly programmed or U/S inverter (not really sure whats up with it)
Incorrect wiring between the Inverter and the Motor
Incorrect wiring of the Motor windings

So thanks again for your time DW, Was extremely helpfull and as usual I learned much from this episode.

Tony, Thanks for the reply, There was no chance of it windmilling but I do know what you mean, Used to have that problem with the air con units at my old site.


So have you connected the motor in Delta now, as per motor plate?




The Vacon manual can be found http://www.crtd.co.uk/ac-drives/vacon-nxl.php

Ensure parameters P2.1.6 thru 10 match the details of the motor plate.
 
Last edited by a moderator:

Reply to A strange fault and a interesting days fault finding.... in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
579
Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
951
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
853
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock