It was clear enough for those that read it properly!!Just to clarify, the garage is attached to the house and the CU is located in the garage.
My apologies if it was worded badly. I will edit the original post to make it more clear
It was clear enough for those that read it properly!!Just to clarify, the garage is attached to the house and the CU is located in the garage.
My apologies if it was worded badly. I will edit the original post to make it more clear
Thanks for your reply.There are lots of variables here, what size cable is feeding your garage? What type of cable is the feed to the garage? What size is the circuit breaker? Is there any RCD protection, if so where is that protection?
There are also computers then there are computers, do you know what sort of current draw they have?
A lot of garages are fed by a small supply cable as most people just want to plug in say a lawn mower and have lights in the garage, you may need to increase the size of the supply cable.
Having just 6 computers you should be ok on the earth leakage just about but if you ever want to add more it might be worth thinking about a separate circuit for future expansion. If you do need to increase the supply cable think about also if you would ever want to put a car charger on the garage wall. What about any possible heaters in the garage?
I know it just seems like you add some more sockets but it really depends on the load requirement and what is currently in place, nobody on a forum can really tell you that so you need an electrician.
hahah no not quite.You're not mining crypto currency are you?!
Thanks, I will definetly look into this!Also to add, you might want to consider lights in the garage with battery back up in case power does go off and you are plunged in to darkness. You can get LED batton lights with that built in for only £40 or so extra.
I think I would be considering a hardwired UPS in the 3000va range.hahah no not quite.
I have multiple servers for different services, some of which I rent out.
From getting quote's for things in the past it's much easier to refer to them as generic computers.
I've thought about a UPS before.I think I would be considering a hardwired UPS in the 3000va range.
it should have plenty of outputs to power your servers and will save you hours of fun the first time you have a 5 second power cut.
his customers get a discount for bringing their own hammer.I'd have thought a UPS would be essential if you are providing paid-for processing power. Do you not have anything in your contracts about availability/redundancy etc?
If this is going to be worth any significant money to you then you might be wise to think about a new CU so you have both surge protection at the supply point (normally part of any new install now) and all circuits on RCBOs so less chance of faults on one circuit taking out the others.I've thought about a UPS before.
Luckily we don't have very many power outages but it's on my list of things to get!

I have copied my own just to strip off the stupid "prohibited actions" like not skipping advertisement crap.Oi! I may be good and old fashioned, but I have never copied DVDs
5th copy or 5th amendment. ? yanks always in front, BS7671 never has more tha 3 amendments. it's them pigeon heads at IET, can't count past their toes.I'll take the 5th...