I'm a trainee in my first year and I can see the best way to do this as the CU is already in the garage would be to stick another ring final on. The maximum power for a pc is going to be 250w. You can run 10 of those and several desk lamps and printers without issue.
It’s not just power you need to think about.

10 pcs, plus 10 monitors, plus a printer, power supplies for peripherals etc all have an inherent earth leakage. Nothing serious on its own, but can soon add up to the 30mA rcd. Considering most trip at about 20mA
 
10 IT appliances on a RCD protected circuit is considered to be the limit to prevent nuisance tripping
 
It’s not just power you need to think about.

10 pcs, plus 10 monitors, plus a printer, power supplies for peripherals etc all have an inherent earth leakage. Nothing serious on its own, but can soon add up to the 30mA rcd. Considering most trip at about 20mA
Why would you need an rcd? Surely he has a main rcd already as part of the CU. Why not just have a type b MCB? As you would A regular ring.
 