ianphilip007

hello

when adding a new circuit (via spare way) to a existing CU with a 30ma rcd main switch (we cant change the board all the time or fit rcbo), do you note as a deviation on cert re (regulation 314) or not write anything ?

many thanks
 
Last edited by a moderator:
30mA main switch? Is it a TT installation? I would say that it wouldn't comply with 314.1 as surely this would cause danger if the whole installation was to lose power i would say the main switch should be a time delay RCD if anything.
 
no not a tt system its a tncs. accept that compliance with 314.1 is not being met, so my question is do you note this as a deviation on cert and advise customer accordingly? ( exisiting board/installation installed to different regulations. 17th not retrospective)
 
Why a time delayed RCD? There is no other RCD to worry about re discrimination. I would say a 30ma RCD gives the additional protection that was already there and is required. I would add the circuit and make a note of what I have done and my considerations on the cert (but then I do write everything down!) I would discuss with customer and expain and note it. Your added circuit will comply with the latest regs. A new board would be ideal (isn't it always) but not necessary IMO. That is my thinking anyway!
 
Last edited by a moderator:
Reg. 314 states that it must not cause danger if a fault occurs on one circuit? With a standard non time delayed RCD main switch surely this would cause the whole house to black out if a single fault occurs on any circuit?
 
that was my thinking too, note on cert as to what has been done and re (314.1) advise customer re nusicance tripping due to single rcd, new board would be grt but not always possible or needed. additional circuit will meet 17th regs as required (rcd protected) existing installation is not required to meet current 17th regs and in my opinion this is where reg (314.1) should be applied to the exisiting CU which predates the 17th.
 
You didn't design or install the existing installation. Responsible for the circuit you're installing. RCD protected, so I would say OK.
 
true lol the lights would go out in a power cut and so would everything else. dont think they have regulated the almighty yet but give them time
 
Reg. 314 states that it must not cause danger if a fault occurs on one circuit? With a standard non time delayed RCD main switch surely this would cause the whole house to black out if a single fault occurs on any circuit?

Yes but it also states you need 30ma RCD protection and by removing that you are leaving it in a "worse" state than when you arrived.
 
perfectly acceptable to add your new circuit. fill in a EIC. just comment on the fact that the CU does not comply with current regs. on to next job.
 
Change a board,danger,warnings ?

Is this a consumer unit that is a melting catastrophe about to happen ?

No, its a unit with a front end rcd,as fitted in millions of homes, including mine, and doing on the whole as fine a job as any cheap and nasty and new twin rcd up to date unit which could be argued is itself a compromise of the intention of the regs itself

There is very little problem, other than slightly more inconveniance than your new units on the perhaps extreemly rare occasions when faults present themselves

I find some of the comments, about changing boards and danger etc on this matter,a little disconcerting

We are told in many posts on this forum, about the perception that the public see themselves as being ripped off when we mention the need for earthing and bonding to do small jobs
That perception may have some justification,with changing consumer units because there is a front end rcd and warning the customer of the imminent danger they are in,unbelievable
 