So the ones I linked to in my last post were metal but also mention external and seem to have rubber seals, are you saying that you think these are okay if used with sealant (that was my plan).
An indoor gland has 2 metal parts, one that fits the box (with a nut inside) and the other that screw on to it clamping the armour wires.
The outdoor SWA glands have a 3rd part, it goes over the armour-clamp and has a sealing ring gripping the cable's outer sheath to keep water out of the armour.
However, the usual SWA glands are
not really waterproof for submersion, etc, as they lack full sealing on the screw threads, and they do not have any sealing washer between the first part and the box. For the gland-to-box you can use silicone or similar that sets. For the screw thread part you can use some grease or Vaseline.
But if using normal engineering grease be aware it is an extreme pressure lubricant so it is easer to over-tighten as the compressive force for a given torque can be 2-3 times higher than dry metal.
The plastic ones are easier to get a good seal with, providing you do not need the higher strength and armour connection, but even they need some sealant between the gland and box as they are not perfect there (the plastic has some ability to compress to match the box surface, but it has to be quite a clean & neat fit to do so).