Also that duct is not outdoor rated. If you are using SWA then you don't need the duct as it can really be buried in most ground conditions without issue.
But as davesparks has pointed out, you need to use the correct glands for the SWA not just to keep the water out (which the plastic ones do) but also to ensure there is a sound electrical connection to the armor (which also has to be earthed, of course). Also you get SWA glands for indoor and outdoor use, obviously the outdoor type with the additional sealing back should be used on any outdoor connections!
If you use the 3-core wire that you propose, then you can get away with a SWA gland at the garage (power feed end) and using one of the 3 conductors at the CPC (i.e. earth wire) to connect to the lights at the far end (assuming they do need earthed which is most likely), and at the light end you can use a plastic gland. But best practice would be a proper SWA gland at both ends.
Also be aware that most 3 core SWA cable has the phase colors: brown, black, grey
You should sleeve the one you use for neutral with blue (as a normal single phase cable has) and green/yellow for the one you use as earth. Practices vary about which colour to reuse, some go for: grey -sleeve blue for N and black - sleeve green/yellow for earth, other the other way. Whatever you do make it consistent!
Also assembling a SWA gland is a bit trickier than the plastic ones as you need to prepare the armor, etc, but there are several youtube videos showing how it is done. I suspect you have not done it before, so if going down that route then practice first on a bit of wire and a gland that you are not needing.
[automerge]1598456277[/automerge]
Also not the burial depth has to be sensible for the ground use - the 60cm often quoted allows for serious spade work, but on an agricultural field you would look at 1.1m or so. If you know it is never more than an ornamental region lightly troweled then a slightly shallower depth is OK but I would not go much less than 40cm.