I have a situation whereby a new build property has had a green electrical cabinet installed at its boundary, and a new 3ph PME supply installed.
There is a 4c 25mm SWA from here to the detached garage, which will house the plant room (3ph ground source heat pump, 3ph PV inverter), and then another 4c 25mm SWA from the garage to the house.
Incoming water is a new polypipe, and there is no gas/oil on site.

Is there anyway to use the PME, or will I need to TT each site??
 
Is 3 phase required in the house? Why not install 5c or run supplementary earth along side swa to futureproof any alterations? Is there any exposed structural steel work that is extraneous in house of garage?
 
Is 3 phase required in the house? Why not install 5c or run supplementary earth along side swa to futureproof any alterations? Is there any exposed structural steel work that is extraneous in house of garage?

Sounds like the cables are already installed.
As long as there are no extraneous parts requiring main bonding in either the garage or house then the PME earthing system can be used.
 
Sounds like the cables are already installed.
As long as there are no extraneous parts requiring main bonding in either the garage or house then the PME earthing system can be used.
No.
The requirements for bonding conductors also apply to the main earthing conductors where PME conditions apply.
 
To my knowledge all pipework in the house will be plastic, but plant room will probably contain copper.
No exposed steels, all rsj's to be boxed in.

House is 3ph in order to to benefit from the 3ph solar PV, and keep it all balanced.
 
If main protective bonds are required then the armour is inadequate to support the bonding. It is assumed a switch fuse disconnector is to be used at the source of supply, the earthing conductor for this can be selected from Table 54.7 without calculation unless the DNO prescribes otherwise. From here the armour can be used as the cpc (assuming bonding is not required), you can verify the suitability of the armour to be used as a cpc using 543.1.3 and the adiabatic equation, it is not likely this will indicate the armour is not suitable. Remember if bonding is not an issue and a switch fuse connector is in place the armour is a cpc and not an earthing conductor.
 
"542.3.1 Every earthing conductor shall comply with Section 543 and, where PME conditions apply, shall meet the requirements of Regulation 544.1.1 for the cross-sectional area of a main protective bonding conductor." (Note quotation marks)
Irrespective of whether there are extraneous-conductive-parts or bonding conductors, the requirements are for the CSA of the main earthing conductor to be determined by use of Table 54.8, where the earthing conductor is other than copper, the CSA shall afford equivalent conductance. (Note lack of quotation marks)
 
On the earthing conductor bit, I've been struggling with this. Opening GN8, page 37, it reminded me "the earthing conductor of an electrical installation is the protective conductor that connects the means of earthing (DNO in this case) with the MET of the installation ... There is only one such conductor in each installation."

So my thoughts are : Assuming the cutout, service fuse and meter are in the garage, then the MET is likely there and the cable linking MET to cutout is the earthing conductor for the whole site. Since we know the DNO incoming is 25mm, the earthing conductor could be selected as 16mm, being the bigger of Tables 54.7 and 54.8, if I've understood correctly. Then the cable from garage to house needs to provide CPC and protective bonding conductor (if required). CPC could be selected from Table 54.7 to be the adiabatic equivalent of 16mm copper, and for this SWA armour is ok. The protective bonding conductor (if required) could be selected from Table 54.8 to be the conductive equivalent of 10mm copper, which the armour does not meet.

Please let me know if I've stuffed this :)
 