tommytippy

Hi,

I've just recently changed a C/U that had a supply to a garage via 2 core 2.5mm SWA. The cable on the old set up was coming from a main switch that was seperate from the house c/u. The garage has a small c/u supplying 1 socket and some lights.

I havn't reconnected the garage supply because i'm not sure if it is going to comply with 17th Ed. I've got a new c/u for the garage that has RCD protection and the new c/u in the house is also fully RCD protected.

Would it be justifiable to put the supply cable on its own circuit in the new house c/u where it is RCD protected and use the SWA for earthing?? Is a 2.5mm cable big enough?? The garage won't have any big loads, probably just the lawnmower.

I'm trying to get this job sorted so I can use it as an example for inspection, any feed back would be very helpful.
 
If your supply is not coming from the house CU which is fully RCD protected then your unit in the garage will need RCD protection for any sockets fitted if not a ring ensure to put it on a 20A mcb.

What is protecting the 2.5m cable coming into the garage.


Chris
 
I have a new c/u for the garage which has RCD protection (yet to be installed). The 2 core 2.5mm SWA only had the protection of the main switch and was burried in the ground.

I'm happy that the garage circiuts will be RCD protected once in install the new c/u, but does the SWA from the house to garage need RCD protection? And is 2.5mm sufficient enough as the supply?
 

Reply to Another "supply to garage" question! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock