Evening all,

Just started the first fix in a purpose built block of 4 flats. Gas and water supplies to each unit are run in HDPE and the water/heating installation in each flat are almost entirely in plastic too - save for short copper tails to the rads ( 20cm ish) and taps and the hot/cold at the boiler (80cm ish). My question is are main bonds required ? I can't see how they'd be effective even if I was able to install them anyway.

What's the best way to cover this on the EIC as I don't want to put down as a departure from the regs ?

Any suggestion gratefully received.

Thanks
 
I can see the argument for not bonding the gas, but would personally insist that a plumber installed a short section of copper to provide main bonding point. After all water will conduct, the palstic pipe just makes it an insulated conductor.
 
Whatever happens i always run the cables in regardless, plus the gas should be bonded anyway.
 
I can see the argument for not bonding the gas, but would personally insist that a plumber installed a short section of copper to provide main bonding point. After all water will conduct, the palstic pipe just makes it an insulated conductor.

Click on either of the web address, this article may help, plastic pipe installation do not require bonding, even if short lengt of copper are used at the terminations.

Hep2O® - Electrical Earth Bonding of Plastic Plumbing Systems

www.------.org/publishing/.../pre14-earthing-plastic-pipes.cfm?...
 
i maybe wrong but i thought there was an resistance limit between pipes that should be checked to assess if the pipes needed bonding or not.

YES FOR METAL INSTALLATION Gn.3 states 0.005 ohms, not for plastic, as P cook state resistance is likely to be thousands of ohms.
 
Zupos just read the post

If the incomming supply of both Gas and Water to the istallation are plastic then no need to bond as thay are insulated. I would not put a bond on anyway as you are just intrudcing them un-necisseraly into the electrical system.

the figure from GN3 is 0.05 as that is the will ensure that the main protective device will rupture within 0.4 seconds assuming its a 100A hrc in a domestic property.( see appendix 4 of BRB)

I can see the argument for not bonding the gas, but would personally insist that a plumber installed a short section of copper to provide main bonding point. After all water will conduct, the palstic pipe just makes it an insulated conductor.


why put a bond on a short lenght of copper and bond that?
You made the statement that water can conduct but its in an insulated PVC pipe. For the water to conduct the fault current has to pass trough the insulated pipe in the first place. why put a bit of copper in the system. you are only extending the electrical system and therefore increasing risk.
 
Last edited:
The gas must still be bonded as its continuous throughout the house and wont be in plastic.

It also says (somewhere) that IF the installation is metal and the incoming is plastic, then it should still be bonded.
 
Zupos just read the post

If the incomming supply of both Gas and Water to the istallation are plastic then no need to bond as thay are insulated. I would not put a bond on anyway as you are just intrudcing them un-necisseraly into the electrical system.

the figure from GN3 is 0.05 as that is the will ensure that the main protective device will rupture within 0.4 seconds assuming its a 100A hrc in a domestic property.( see appendix 4 of BRB)


Sorry typing error slipped in too many zero
 
The gas must still be bonded as its continuous throughout the house and wont be in plastic.

It also says (somewhere) that IF the installation is metal and the incoming is plastic, then it should still be bonded.


If there is continuous metal pipework in the house it should have a bond on it agreed !

how i read the post was it was a plastic incommer and plastic pipework apart from short lenghts to the radiatos. (like my house) In this case why bond everything as you are just introducing it to the electrical system. As there is plastic pipework then there is no earth path so no fault current. If however its only a short lenght of plastic puipework used to get round tight corners i would consider a little cross bond.
 
This is how i understand the regs:

If the incoming services are plastic and the pipework inside is completely plastic then no bonding is required.

If the pipework inside has metal parts, then the 0.05ohm rule applies (to extraneous and expose metal parts within areas of special locations and if not using RCD's) and then should be bonded if the reading is above this level. This being that above this level there could be a dangerous potential difference because of the high resisitance between pipes. If a lower resistance than 0.05 is read then this would be unlikely to cause a dangerous potential difference.

I stand to be shot down in flames though!
 
nearly there

If there was no potential difference the pipework would be live though.
What you want is a low earth path creating a very high fault current and so ensuring the overcurrent protective device will blow in time. The ESC and other agree on 0.05 as this will cover a 0.4 disconnection time on a 100a HRC will will be about the largest you will get in a domestic property.
 
Whatever happens i always run the cables in regardless, plus the gas should be bonded anyway.


Yep I would just install them and coil em up nearby at both ends , better to have and not need than vice versa after the plasterer has gone, lends for a better nights sleep. :D
 
The gas must still be bonded as its continuous throughout the house and wont be in plastic.

It also says (somewhere) that IF the installation is metal and the incoming is plastic, then it should still be bonded.


Explain why the gas WOULD not be in plastic, matey has already said they are in plastic
 
i had my niceic inspection one of the jobs was some flats that had been referbed same thing with the gas and water. but he insisted i run the earths to the incoming position just in case of any later alterations. so i would say run the earths in but dont conect them.
 
What you want is a low earth path creating a very high fault current and so ensuring the overcurrent protective device will blow in time. The ESC and other agree on 0.05 as this will cover a 0.4 disconnection time on a 100a HRC will will be about the largest you will get in a domestic property.

Sorry Scotsparky, but that isn`t the reason that 0.05 ohms is stated as the max permissible resistance between extraneous & exposed conductive parts - which is what is being discussed here. The correct reason was actually given by Markthesparky.
What you`re referring to is applicable where the required disconnection times cannot be achieved by breakers/RCD`s so supplementary bonding is utilised to ensure disconnection within the prescribed times.

Altho the need to ensure adequate conductance is common to both, in the context of Main Protective Bonding to water & gas services, it`s done to ensure no dangerous differences in potential exist between the various conductive parts - achieving equipotentiality. :)

T
 
Hi all.
Why does water and gas cause a major headache for electricians. Do we deserve this agro ???? The point of all this bonding conductor stuff ( as we already know ) is to cover ourselves from pipework that is exposed to human touch, getting a potential that could be harmful with reference to earth.

Tell me why plumbers aren't made responsible for ensuring their own installation is correctly earthed ?

Do what you can. As long as you can walk away from the site and be confident you've done what you are expected to do, then that's it.

I was told that if incoming pipework was not metallic ( so no conductive path back to earth ), then main bonding wasn't necessary.

But, like you say, what about radiators with a minimal amount of copper pipe work attached ? Well, just like previous wiring regs, which insisted that metallic windows and doors required bonding, things went just too far !!!!!

I would say that radiators fed from plastic pipework don't need bonding. As long as the situation is in writing describing this, then you are ok.
 
Hi all.
Why does water and gas cause a major headache for electricians. Do we deserve this agro ????

Friday, prior to starting job, checked bonding 10mm & in place...
Gas - no prob.
Water - at what appears to be main stopcock, no bonds in sight...

Upon enquiring, kitchen was fairly recently refurbed. Made a nice neat job of hiding the bond(s) completely behind sink units. Say bond(s) due to how they`d very thoughtfully bonded hot as well as cold (conscientious or what :rolleyes:) but unfortunately placed them in totally inaccessible position, >600mm from incomer & after 2 branches. Classy...

Measured 0.03 ohms.

Thankfully, the peeps at Elecsa are reasonable folk & take these things in their stride... mark down as deviation & carry on :)


But, like you say, what about radiators with a minimal amount of copper pipe work attached ?

I would say that radiators fed from plastic pipework don't need bonding

Usually not. Whenever in doubt, do IR test between known earth & extraneous part - anything above 20-25k, don`t bond.
 
Evening all,

firstly a huge thanks to everyone for the comments and suggestions - I think this is where this forum and its contributors are at their best.

Secondly, apologies if I've appeared a bit 'mute' on this thread - unfortunately I've been working late this evening and only just got to the PC.

Based on the info I've been given and references from NIC, Paul Cooke etc, I'm sure I don't need to run in main bonds, but after today's experience of the plumber ( same bloke, different job) I'm underwhelmed to put it mildly. Consequently as wisely advised in the thread, I'll run them in anyway just to be on the safe side, even if only for future possible need. Might be overkill, but I'll sleep easier.

Thanks again lads.
 
Of course, problems may well arise in those special locations ( bathrooms ), where you have to ensire that any exposed conductive parts ( take your pick from piepwork and radiators ) are bonded. So you might have to do some supplementary bonding in those loactions.
 
There are various conditions that have to be adhered to and installed by certain persons

Fair enough.

Every day is a school day.:D

Have you got any links or other info on this?

Would be interested to have a read.:)
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
are main bonds required ???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
WILLRUK,
Last reply from
Spudnik,
Replies
28
Views
3,114

Advert

Back
Top