Discuss Attach 1 double socket to CU in the DIY Electrical Advice area at ElectriciansForums.net
pckid57
Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.
I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
Technically you can nick a feed from an already in use mcb.
But if you have a spare slot then just whack in a new 16a mcb for the new plug socket
Thanks for the reply. I'm not sure if I have an empty slot yet. If not is it safe to "Nick a feed from an existing mcb"?
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
Reactions: DPG
So it's okay to run a 2.5mm twin & earth from the existing mcb straight to the new intended socket, which is about five feet away from the CU?
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
Yes that’s fine mate providing it hasn’t already been spured off from the CU
…….and are you sure all is in order with the existing ring circuit, if there is one. A bit of testing wouldn't go amiss.
Yes there is RCD protection. The new socket will only be used to charge s Dyson Hoover.
Put in a new protective device to a spare way requires notification to building control, this is a legal requirement. Some responses to this thread have not considered this.
See #7, this
Hi, no I didn’t consider if it was going to be notified i assumed he was going to comply with regs and I’m new to forum and I can quickly see that people without relevant qualifications may just want to do DIY without it being properly tested and certified so my bad will make sure future responses are compliant
If the new socket is near the CU. Remove one of the legs of the ring from the CU MCB and put it in your new socket. Run a short length of 2.5 T & E from you new socket back to the CU MCB. Thus the new socket becomes part of the ring.
Reply to Attach 1 double socket to CU in the DIY Electrical Advice area at ElectriciansForums.net
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
