Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
 
Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?

Technically you can nick a feed from an already in use mcb.
But if you have a spare slot then just whack in a new 16a mcb for the new plug socket
 
Hi, my Consumer Unit is in a cupboard in my hall. I would like to install 1 double socket only in this cupboard.

I was wondering if I could run the cable to feed this socket from an already occupied 16amp mcb or 32amp mcb from within my CU?
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
 
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
Or preferably just put it on its own circuit as dusty dazzler said
 
Hi, yes you can do that at the consumer unit aslong as you havnt already spured off from your consumer unit the regs say an unfused spur May be connected to the origin of the circuit at the distribution board
So it's okay to run a 2.5mm twin & earth from the existing mcb straight to the new intended socket, which is about five feet away from the CU?
 
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
 
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
…….and are you sure all is in order with the existing ring circuit, if there is one. A bit of testing wouldn't go amiss.
 
Put in a new protective device it would require notification to building control under Part P of the Building Regulations. Connected from the existing ring final circuit it does not, that's the way of it. Do you have rcd protection.
Yes there is RCD protection. The new socket will only be used to charge s Dyson Hoover.
 
Put in a new protective device to a spare way requires notification to building control, this is a legal requirement. Some responses to this thread have not considered this.
 
See #7, this
Put in a new protective device to a spare way requires notification to building control, this is a legal requirement. Some responses to this thread have not considered this.
Hi, no I didn’t consider if it was going to be notified i assumed he was going to comply with regs and I’m new to forum and I can quickly see that people without relevant qualifications may just want to do DIY without it being properly tested and certified so my bad will make sure future responses are compliant
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pckid57

DIY
-
Joined
Location
Scotland

Thread Information

Title
Attach 1 double socket to CU
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
37

Thread Tags

Advert

Thread statistics

Created
pckid57,
Last reply from
westward10,
Replies
37
Views
7,964

Advert

Back
Top