Hi,
Just wondering on thoughts for complying with Reg 528.1 "... a Band I circuit shall not be contained in the same wiring system as a Band II circuit ..."
The current setup has steel trunking running around the walls with conduit coming down from here for network points and plug sockets etc.
What would be the easiest way to keep this kind setup but ensure the regs are complied with?
I've considered something like:
It's only in a small office so not too worried about interference on the network cables, and could swap them for screened cables if needed.
Many thanks for any suggestions
Just wondering on thoughts for complying with Reg 528.1 "... a Band I circuit shall not be contained in the same wiring system as a Band II circuit ..."
The current setup has steel trunking running around the walls with conduit coming down from here for network points and plug sockets etc.
What would be the easiest way to keep this kind setup but ensure the regs are complied with?
I've considered something like:
- Running 2" plastic trunking inside the 4" steel trunking to provide separation (but would get awkward at where the conduit drops are close to one another)
- Adding an extra layer of pvc sleeving over the cat6 cables to give the required level of insulation.
It's only in a small office so not too worried about interference on the network cables, and could swap them for screened cables if needed.
Many thanks for any suggestions