Hi,
Buying a replacement extractor fan. It falls into zone one with the room setup. Looking at two fans. One is rated zone 1 one is rated zone 2 and both have ipx4 ratings from what I can see and from wider reading ipx4 is the requirement for zone one and two?

is the ipx rating all the appliance rating is based on? For 10 quid extra it doesn't matter but it piqued my interest.

TIA

Tom
 
Hi,
Buying a replacement extractor fan. It falls into zone one with the room setup. Looking at two fans. One is rated zone 1 one is rated zone 2 and both have ipx4 ratings from what I can see and from wider reading ipx4 is the requirement for zone one and two?

is the ipx rating all the appliance rating is based on? For 10 quid extra it doesn't matter but it piqued my interest.

TIA

Tom
The way I read it ...701.55 Current Using Equipment:
States that " In Zone 1 only the following fixed and permenantly connected current-using equipment [ which includes ventilation equipment] shall be installed, provide it is suitable for installation in Zone 1 according to the manufacturer's instructions."
So it's not just the IP rating, it's whether the manufacturers instructions states it is suitable for Zone 1
 
The way I read it ...701.55 Current Using Equipment:
States that " In Zone 1 only the following fixed and permenantly connected current-using equipment [ which includes ventilation equipment] shall be installed, provide it is suitable for installation in Zone 1 according to the manufacturer's instructions."
So it's not just the IP rating, it's whether the manufacturers instructions states it is suitable for Zone 1
Thanks for your thoughts on it. It seems weirdly vague to have some rules like the ipx4 with the addendum of on the proviso it's backed up by a 30ma RCD for zone 1. Then rely on manufacturers ratings too.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
York
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Bathroom extractor fan ipx query
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
Tom York,
Last reply from
Tom York,
Replies
2
Views
932

Advert

Back
Top