we had a scenario like this a while back....but in this case the thermal cutout within the tranny was constantly bringing the lamps off....then in a while back on they came.....turned out the origional installers had joint boxed a load of lamps off just 2 trannys..........

Some of em just ain't got a clue mate have they lol.
 
Can you not take a voltage reading on the load side of the trannie at the terminals of each light fitting ? Also agree looks like you have lost the neutral return on leg . depending how they have been wired via jb,s or wago,s if straight into light fitting they are normaly quite tight for termination if daisy chaining and quite often will come out especilly as you say some lamps have been changed recenctley i would be looking at that area 1st
 
Last edited by a moderator:
Some of em just ain't got a clue mate have they lol.
thing is though is we found it quite funny as the lady was explaining to us that they had a downstairs loo where the lighting was also of this arrangement....she said that she daredn`t spend long in there as all of a sudden the lights would go out............
 
Thank you specialist will give it a try good advice given cheers mate.

No probs mate: Good luck & Let us know what happens, you need to arm yourself with a Meter or 2 pole tester for fault finding though. They take the guesswork away.
 
thing is though is we found it quite funny as the lady was explaining to us that they had a downstairs loo where the lighting was also of this arrangement....she said that she daredn`t spend long in there as all of a sudden the lights would go out............

What & you did'nt tell her she had a Ghost ? :biggrin5:
 
What wattage are your lamps?
Notice in post 12 you say one of your transformers is rated at 65w and the other is 60w?
 