You could fit an enclosure with an RCD instead of an RCD FCU.Its annoying as it looks like i will have to RCD at the CU end to include the entire lighting circuit which means I'm risking running into pre existing faults that have to be explained to customer.
Who would be happy to use an RCD spur noted as a departure on the cert given that I'm using the RCD as a means to ommit the need for supplementary bonding?
Sparky ninja posted a blog about this issue. It doesn't sound like a mistake or something that will be changed. If it doesn't provide the correct isolation we shouldn't use them as it doesn't give the same level of safety. Please correct me if I am wrong and they are now proposing this for amendment 2.Basically the IET made a MASSIVE mistake MASSIVE, by not including bs7233 in reg 531.3.6, this is why when the new amendment that comes out in march 2022 will put it right. So the departure they want us to include on our certs is due to there MASSIVE mistake. Carry on using just include there mistake (we should get a refund for this one)
The biggest problem is that there is no one in a suitable position of authority willing to make a clear unambiguous statement on when and when not they should be used. Instead we get carefully worded statements that are more concerned with covering themselves, while not upsetting the manufacturers who make these products, so that they can't be used against them in a court of law.Sparky ninja posted a blog about this issue. It doesn't sound like a mistake or something that will be changed. If it doesn't provide the correct isolation we shouldn't use them as it doesn't give the same level of safety. Please correct me if I am wrong and they are now proposing this for amendment 2.