One of the IET Q&A had an answer, in a rather convoluted way, saying:No, there was a thread about it a bit ago, but then there are conflicting threads to say that it wont.
"RCDs to BS 7288 are not recognised for use as an RCD by BS 7671:2018. See Regulation Group 531.3.4.
Clause 1 of BS 7288:2016 states “SRCDs are intended for use in circuits where the fault protection and additional protection are already assured upstream of the SRCD.”
Further, Clause 0 of BS 7288:2018 states the devices are only suitable for additional protection against direct contact, and therefore cannot provide fault protection (e.g. where disconnection times cannot be met in a circuit), nor would they be recognised for additional protection against fire due to short circuits in appliances or flexible cables connected to the socket-outlet or connection unit.
However, there is nothing to stop accessories containing SRCDs to BS 7288 being fitted in electrical installations complying with BS 7671, as they comply with the relevant standards, although as stated the RCDs within them cannot be recognised for the functions of fault protection or additional protection for the purses of BS 7671."
Not having a copy of BS 7288 to look at, the only thing that I can really see from the above is the rather odd statement that they cannot provide 'fault protection', only shock protection. But why that is has not been elaborated anywhere I have seen.
I don't know if it comes down to breaking capacity, etc, but I would be happier with one for shock protection than not, assuming the circuit is otherwise capable of meeting disconnection on the MCB/Zs results, etc.