Protecting a whole circuit has got to be a better solution most of the time and the srcd's aren't cheap either.

The op should be testing the circuit regardless and issuing the customer with a certificate of tests confirming it is safe for the alteration.
 
While doing some CPD, GN8 amd. 3 has a section in it suggesting their use:

Section 8.7 "Low voltage socket-outlets (for example, 230 V) may be installed not closer than 3 m horizontally from the boundary of zone 1, provided they are protected by an RCD having a rated residual operating current, IΔn, not exceeding 30 mA, in accordance with Regulation 415.1.1. In cases of retrofit, this requirement could be met by the provision of a socket-outlet with an integral residual current device, as shown in Figure 8.6, or, alternatively, the circuit could be fitted with RCBO protection."

It is a poor situation, you would of course need an attractive big yellow label too ?
 
  • Like
Reactions: pc1966 and Dartlec

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Rochdale

Thread Information

Title
Bathroom RCD protection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41

Advert

Thread statistics

Created
Jm1980,
Last reply from
Aaron b,
Replies
41
Views
11,653

Advert