Jm1980

-
Reaction score
16
Looking at a bathroom modification and wouldn't mind some input on the need for RCD protection.

Bathroom has existing light and wall fan. Customer wants downlights fitting and ive also said the fan needs an isolator as it currently doesn't have one. No other electrical circuits in the room. No supplementary bonding is present either and as the room is nearly finished, adding any is difficult.

Firstly, all work is outside the zones so my understanding is that part P doesn't apply?

The circuits obviously need RCD protection as per 18th and also as i have no supp bonding present. CU is a split load 16th edition style with upstairs and downstairs lights on the non protected side. The option to run a new bathroom dedicated circuit isn't feasible due to difficulty of run and customer not wanting this. As i see it then that leaves a couple of options.

1, switch the upstairs lights onto the RCD side at the CU thus protecting the entire circuit and thus the bathroom. This seems a good option although I'm risking any faults already present giving me RCD issues (borrowed neutrals and the like).

2, An easier option seems to be to run the lighting circuit into an RCD fused spur and then from this create my bathroom lighting and fan wiring. I see conflicting opinions on the RCD fused spur option though especially since upgrade to the 18th.

Any opinions appreciated.
 
The building regs DO apply, INCLUDING PART P

You intend to work in a special location
Also, the work involved is beyond that of a minor works certificate.

EDIT, @westward10 has pointed out this is incorrect.
Back to school james!
 
Last edited:
Hi James

I was under the impression that as the work is outside the zones that the work is not notifiable, that's the last NICEIC guidance i remember on it unless it has been changed?
 
Off the top of my head according to Part P it is only notifiable if the works are carried out within the boundaries of the zones, Part P only deem these areas as a special location. Outside of these it does not apply.
What make is the consumer unit.
 
If changing to a RCBO, as you have already mentioned, you may have problems with borrowed neutrals on a light. Most prob the landing light. (I would have the same in my house) If the customer doesn't want his walls messing to rewire switches then you could always change the light to be controlled by a wireless switch, like Quinetec.
 
Cheers, definitely an option but moving the mcb onto the rcd side probably easier (space in CU) although id lose a bit of installation division. My main worry is inheriting faults on other parts of the circuit if i rcd the lot.....

Any thoughts on using the rcd fcu option?
 
Any thoughts on using the rcd fcu option?

As @westward10 has already mentioned, these are not currently listed in BS7671.
There was a thread somewhere saying that they may be adding it but it hasn't happened.

Strange that these are still being manufactured, if they are not to current regs though, or is it ok just to put them down as a 'departure from BS7671'?
 
On a wider point isnt this poor by the reg writers?

Not got my 17th to hand but were 7288 devices listed for additional protection in there? Presumably so.

The need for rcd’s on bathroom circuits must throw this conundrum up often so you would think this would be clarified with reasoning one way or the other by those that write the regulations.
 
On a wider point isnt this poor by the reg writers?

Not got my 17th to hand but were 7288 devices listed for additional protection in there? Presumably so.

The need for rcd’s on bathroom circuits must throw this conundrum up often so you would think this would be clarified with reasoning one way or the other by those that write the regulations.

Pretty sure it's been stated that it will be corrected in future versions. Or have I imagined that?
 
Pretty sure it's been stated that it will be corrected in future versions. Or have I imagined that?

No, there was a thread about it a bit ago, but then there are conflicting threads to say that it wont.
 
On a wider point isnt this poor by the reg writers?

Not got my 17th to hand but were 7288 devices listed for additional protection in there? Presumably so.

There is no mention of BS 7288 in either the 17th or 18th edition.
 
On a wider point isnt this poor by the reg writers?

Not got my 17th to hand but were 7288 devices listed for additional protection in there? Presumably so.

The need for rcd’s on bathroom circuits must throw this conundrum up often so you would think this would be clarified with reasoning one way or the other by those that write the regulations.
The 17th Ed never suggested the type of device which should be used just that it should be 30ma with quoted tripping parameters.
 

Reply to Bathroom RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
606
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
369
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
334
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
659
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock