The machine is a Sunnen CK-21-E used for Honing. I cannot find any manuals but ill post the tag. I dont believe its multi-voltage which would make this a lot easier for me. It says 480V and its pulling 12 Amps full load.
Location is in a warehouse. Only power nearby is 2ea. 208V panels both being supplied by a transformer. 408/208V ill send the spec for that also. Id like to get the power from the 480V side of the transformer as its very close to the machine but not sure if it will effect the 208 panels . The transformer gets its power from another room . That panel has no room for additional breakers.. The more i think about it the more obstacles Im facing .
If i can make room in that panel could i pull wire to the transformer and through it (not connecting to anything) and run conduit to the the machine?
Actually I would need a disconnect too right? since the panel is in another room? Not in line of sight ?


Location is in a warehouse. Only power nearby is 2ea. 208V panels both being supplied by a transformer. 408/208V ill send the spec for that also. Id like to get the power from the 480V side of the transformer as its very close to the machine but not sure if it will effect the 208 panels . The transformer gets its power from another room . That panel has no room for additional breakers.. The more i think about it the more obstacles Im facing .