Search for tools and product advice,
Discuss Blooming borrowed neutrals in the Australia area at ElectriciansForums.net
A
aaronstuart
Had a crap day, replaced a cu in a small terraced house.
No problems until dinner, done all tests with good results, ring main on one side of rcd, and lights on the other rcd ( only 1 x lighting circuit ), and both rcd's were tripping.
Found it was a borrowed a neutral from the ring main ( JB in loft ) feeding the extractor fan!!!!!!:mad:
You have my sympathy mate, we are always being hampered by previous work by the boys in tall hats and spurs----makes you mad doesnt it ?
sparkylad
ya-haven't had much trouble with this sort of thing but
- nothing will show across circuits until the load is switched on/in-circuit
- and then either or both rcds can trip
Luckily the first time I've come across this..........borrowed neutral on the up/down lights fairly often......just a pain in the rear.....
Reply to Blooming borrowed neutrals in the Australia area at ElectriciansForums.net
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
8K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
