Had a crap day, replaced a cu in a small terraced house.
No problems until dinner, done all tests with good results, ring main on one side of rcd, and lights on the other rcd ( only 1 x lighting circuit ), and both rcd's were tripping.
Found it was a borrowed a neutral from the ring main ( JB in loft ) feeding the extractor fan!!!!!!:mad:
 
You have my sympathy mate, we are always being hampered by previous work by the boys in tall hats and spurs----makes you mad doesnt it ?


sparkylad
 
ya-haven't had much trouble with this sort of thing but

- nothing will show across circuits until the load is switched on/in-circuit

- and then either or both rcds can trip
 
Luckily the first time I've come across this..........borrowed neutral on the up/down lights fairly often......just a pain in the rear.....
 

Reply to Blooming borrowed neutrals in the Australia area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K
Evening all. I did an EICR recently and then changed a consumer unit. As part of the EICR process I take off around 25% of all accessories to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock