Hi guys, I need to bond the gas and water at a friends house..never done it before as I worked mainly on sites. My times just out, where’s the best place? Gas meter is outside in a Box so would I just clamp onto the metallic side just before it enters the house? And the water, not entirely sure where it enters the house..any help would be appreciated thanks
 
Last edited by a moderator:
Gas within 600mm of the point of entry to the building, water as close as possible on the consumers side of the SC.
But as above, check bonding is required, plastic incomers mostly negate the requirement for main bonding.
 
main bonding yes
So say for all CU changes, EICRs etc, you test the Gas and Water requirements, and not just say bonding in place of not as the case maybe? Could you point me the the Regulation that endorses your claim please?
 
Last edited:
10mm Main bonding for the gas in the meter box is fine. On the consumers side of the meter rather than the distributor.
As for water, you would need to find the stop cock inside the house. Ask your friend as most customers know where their stop cock is. If you can see a plastic pipe feeding into the stopcock then I doubt it will need bonding as this will be an insulating section where it enters the house.
 

Reply to Bonding Gas and water mains. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
What are the regulations requirements on Earth bonding ? I am currently planning a 1st fix re wire I have the following setup Gas Meter...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock