T
tbs1983
My 2394 tutor says if you do a job (for example add a new circuit) and the water/gas etc is not bonded as per regs, that you should point it out to customer, if they choose to have it done then great, if they say no, you just write it in the 'comments' section on the EIC and you are covered.
I was always under the impression (since 17th edition was released) that it was an absolute must and there was no get out clause as he suggests.
Who is right?
you are right. if earthing/bonding is inadequate or non-existant, then you either fix it or walk away. there's no get-outs. and that goes back way before 17th, as well.
It depends on who you talk to and how you interpret the regs... I was always under the same impression as yourself..
131.8, does say that earthing and bonding arrangements for the installation should be adequate before carrying out any work...
132.16 in the bgb. are you still using the brb?
No Im on the green ;) .... googled for the answer instead of leaving my seat to hoke out bs7671 on a friday night.. now realizing the post was from red book ;)
haha. i just remembered the reg. no, as it came up in a discussion a few weeks ago.
i refuse to subside any more new range rovers, BMWs, mercs, etc. for them suits at the IET. i'll just scribble a few notes in the back of my bgb... do me till i hang up my MFT.
131.8 says
Moved by BS7671 2008 Ammendment No 1 to 132.16
tbs
Here is a direct quote for the end part of 132.16 that guides our actions which says what you stated,,with the little bit on the end that often gets missed out,but it is important
quote
Furthermore the earthing and bonding arrangements if necessary for the protective measure applied for the safety of the addition or alteration,shall be adequate
131.8 says
tbs
quote
I was just about to make exactly that point. If the addition or alteration does not rely on bonding for its safety, then no need to assess or upgrade the bonding. Same applies to earthing. Installation of class 2 equipment comes to mind.
It is early morning here, and only on my first coffee of the day, but what are you saying here?? That if an RCD is in place no need to worry ourselves with bonding and earthing??
Since when, does the use of Class 11 equipment, or accessories, have anything to do with the supplying circuit, that will always need to be Class 1 (eg, ...Earthed) to comply with BS 7671...
It seems we have divided opinion and the regs are not as clear as they should be on the matter
This is a quote from ESC regarding a question on the main bonding of a TN-CS system as to is upgrading neccessary. "Not necessarily. If the existing 6 mm² bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not require to be upgraded."
Also:Is it acceptable to add an item of equipment of Class II or all-insulated construction, such as a smoke detector, to an installation that has inadequate main protective bonding?
Yes.
Regulation number(s): 132.16
  • 132.16