Well, if you don't need an electrician, you do need to calculate the starting current of the motor, using your knowledge of motor and mechanical load characteristics and the starting arrangement used in this lift. Having determined the current and the acceptable voltage drop, and the likely upstream voltage drop from the Zpn at the DB, you can decide whether the tightest constraint is VD during starting, and hence whether the cable is to be sized on that or the load current. Then, size the MCB to satisfy both the starting, running and disconnection requirements having calculated Zs at the lift using your choice of CPC.
BTW, what phase-sequence interlock is used on this lift?