p11jor

Hi there going to check a fault out tomorrow its a comercial building with a fault on the brick lights. They aparantly are fed through a time clock to a contactor then out to the brick lights.

They are having a fault that when the lights go out on the time clock the mcb will trip.....has anyone experienced this before?
 
A fault on something supplied by the normally closed aux on the contactor (if there is one) maybe.....
 
Probably an incorrect contactor not rated for inductive loading (if the lights are inductive)... or the contactor is mechanically faulty and dosn't drop out fast enough you will get a back emf flash over across the contacts this can trip mcb's....

Can you give us more info .. lamp size/type, no' of fittings etc etc
 
A fault on something supplied by the normally closed aux on the contactor (if there is one) maybe.....
Not sure you thought that one through Marvo... how would you reset the mcb if the fault was present through a N/C aux...
 
Dunno, it was a completely uneducated guess, he didn't give much info or say if would reset or not.
 
Well hopefully we will get some feedback to satisfy our minds or its another 5mins of our lives wasted :angry_smile:
 