I've told him to get a sparks in to do it I obviously haven't got the knowledge or experience in this area. I'll meet you lot in the pub as well I think! Thanks everyone
MFT wont do Zs, can do Ze and (r1+r2)/4... Seems like a long way round for me. I was planning to disconnect all cpcs on the circuit, untwist them all, then put wander lead on cpc leg 1 and test continuity at each socket, until I find the first socket in the ring, then do the same with the second cpc on leg 2 until I find the last socket in the ring. Once I've confirmed continuity between CU and first and last sockets I will move on to test cpc between each socket. Would this be the logical way to do it or a long way to do it?! - Also, would this not be the reason the RCD is tripping? Or will I need to locate a N-E / L-E fault somewhere as well? Thanks for your help everyone!
Zs = Ze + (R1+R2) / 4 - So if I did this equation for each socket, the one (or more) with the high readings will be the culprit(s)? Is that what your saying?
FFS, no it isn't.
Zs = Ze + (R1+R2) / 4 - So if I did this equation for each socket, the one (or more) with the high readings will be the culprit(s)? Is that what your saying?
Page 101 OSG states: The earth fault loop impedance (Zs) is required to be determined for the furthest point of each circuit. It may be determined by: direct measurement of Zs, or direct measurement of Ze at the origin and adding (R1 + R2) measured during the continuity tests (10.3.1 and 10.3.2) (Zs = Ze + (R1 + R2). If you look at 10.3.2 page 94 it states: The readings obtained at each of the socket-outlets wired into the ring will be approximately one-quarter of the resistance of the line plus cpc loop resistances, i.e. (r1 + r2)/4.
OK, the CPC being split is highly unlikely to be the cause of your RCD fault, however, here is a very quick way of finding your earth fault.
Get a socket tester (3 neon variety)
Unplug everything from the ring main
Disconnect 1 leg of the CPC at the CU
Go around each socket in turn with the tester, at some point you will go from a fully serviceable ring to a 'no earth' indication. Or vice versa.
Stop and investigate further
Simples......
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?


Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?