I've told him to get a sparks in to do it I obviously haven't got the knowledge or experience in this area. I'll meet you lot in the pub as well I think! Thanks everyone
 
As said that broken cpc will not cause that rcd to trip, you need to do some basic testing pound to a penny short circuit across any 3 poles.
 
Utter ********. How can it possibly know it's Zs and not Ze for one!

MFT wont do Zs, can do Ze and (r1+r2)/4... Seems like a long way round for me. I was planning to disconnect all cpcs on the circuit, untwist them all, then put wander lead on cpc leg 1 and test continuity at each socket, until I find the first socket in the ring, then do the same with the second cpc on leg 2 until I find the last socket in the ring. Once I've confirmed continuity between CU and first and last sockets I will move on to test cpc between each socket. Would this be the logical way to do it or a long way to do it?! - Also, would this not be the reason the RCD is tripping? Or will I need to locate a N-E / L-E fault somewhere as well? Thanks for your help everyone!
 
FFS, no it isn't.

Page 101 OSG states: The earth fault loop impedance (Zs) is required to be determined for the furthest point of each circuit. It may be determined by: direct measurement of Zs, or direct measurement of Ze at the origin and adding (R1 + R2) measured during the continuity tests (10.3.1 and 10.3.2) (Zs = Ze + (R1 + R2). If you look at 10.3.2 page 94 it states: The readings obtained at each of the socket-outlets wired into the ring will be approximately one-quarter of the resistance of the line plus cpc loop resistances, i.e. (r1 + r2)/4.
 
OK, the CPC being split is highly unlikely to be the cause of your RCD fault, however, here is a very quick way of finding your earth fault.

Get a socket tester (3 neon variety)

Unplug everything from the ring main

Disconnect 1 leg of the CPC at the CU

Go around each socket in turn with the tester, at some point you will go from a fully serviceable ring to a 'no earth' indication. Or vice versa.

Stop and investigate further

Simples......
 
Zs = Ze + (R1+R2) / 4 - So if I did this equation for each socket, the one (or more) with the high readings will be the culprit(s)? Is that what your saying?

Page 101 OSG states: The earth fault loop impedance (Zs) is required to be determined for the furthest point of each circuit. It may be determined by: direct measurement of Zs, or direct measurement of Ze at the origin and adding (R1 + R2) measured during the continuity tests (10.3.1 and 10.3.2) (Zs = Ze + (R1 + R2). If you look at 10.3.2 page 94 it states: The readings obtained at each of the socket-outlets wired into the ring will be approximately one-quarter of the resistance of the line plus cpc loop resistances, i.e. (r1 + r2)/4.

I think DJ O's point was that you have confused R1 and R2 with r1 and r2. If you're going to use symbols and abbreviations, using the correct ones is important.
 
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?
 
OK, the CPC being split is highly unlikely to be the cause of your RCD fault, however, here is a very quick way of finding your earth fault.

Get a socket tester (3 neon variety)

Unplug everything from the ring main

Disconnect 1 leg of the CPC at the CU

Go around each socket in turn with the tester, at some point you will go from a fully serviceable ring to a 'no earth' indication. Or vice versa.

Stop and investigate further

Simples
......

I like your style, Sergei.
 
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?

There isn't much of a difference, people just tend to get a little bit muddled up with the terminology :)

r1 is the end to end of the line conductor
r2 is the end to end of the CPC.

R1+R2 is cross connecting the two and testing together.

r1+r2 is a myth :)
 
Really? I didn't realise there was a difference between r1 r2 and R1 R2. My bad! What does the capital letter version stand for?

Only reason we've not got "Gasp..." and "I'm out of here...", is that it's late.

r1 and r2 are end-to-end resistances of ring circuit line and cpc conductors. R1 and R2 are resistance from origin of circuit to furthest point (in the case of a ring, this is the centre) of line and cpc. Not the same thing at all!
 
Oh wow! I didn't know that. Thanks! I'm not an electrician just yet as you have all probably gathered, I'm still at college so I'm learning every day. I have another question, slightly off topic: I was having this debate with my teacher/lecturer... He says that if you have a conductor, say 50m long, and you measure continuity between one end and the mid point (25m) you will get half the ohms value of measuring the full length of the cable. I thought that the extra copper would effect the half way reading? Would the value be half?
 