Zs = Ze + (R1+R2) / 4 - So if I did this equation for each socket, the one (or more) with the high readings will be the culprit(s)? Is that what your saying?
Also, would this not be the reason the RCD is tripping? Or will I need to locate a N-E / L-E fault somewhere as well?
No, lack of continuity on a cpc will not be the reason for tripping of an RCD. What was your reasoning for thinking this?
Yes, you will need to locate a N-E or L-E fault.
time to get my coat.
aarrrghh. twisted cpc's . the work of muppets.
Do you mean when cpc's are twisted along their entire length and fed down the same sleeve?