Discuss BS 1361 50A ZS in the UK Electrical Forum area at ElectriciansForums.net
Anyone know the ZS for an 1361 or BS 88-3 50A fuse. All the tables I find have n/a. I phoned the maker and was told there are no listed ZS' for a 50A and to take the difference between the next closest sizes (45A & 60), surley thats not proportional ?
work it out. if the current required to blow the fuse in the required time is, say, 5In, then max. Zs = V/ 5In.
So i need to find out the fusing factor (the ratio of the In to overcurrent to operate in 0.1 secs) of a bs88 -3.
I need this factor for the formula that telextric has mentioned, where do i get the fusing factor from ? So far all i can find are the factors for B, C, D type MCBs ? Its not 1.45 is it ? Thats for cable :eek:
why 0.1sec? generally, anything over 32A needs to blow in 5 secs. to comply with BS7671.
The current required to blow the fuse in the required time (5 secs) but thought quicker the better but maybe not such a good idea as itll skew results, so yeah 5secs it is. I cannot find no graphs/tables in relation to 50A. Overcurrent needed to blow the fuse in 5 secs ive so far found out can be calculated if you get the fusing factor (which each type of fuse has), where do I find this do you know ??
We could do lottery pick - easier than finding that football ...
My pick is 0.927 Ohms for 5 sec on BS882 50A, from 248A guesstimate.
Reply to BS 1361 50A ZS in the UK Electrical Forum area at ElectriciansForums.net
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
6K
V
Hey guys, i have started to do some inspecting and testing, i am finding it very interesting although the certification part is a little confusing...
4K
Hello Gents Once again I’m looking for your expertise to resolve the following application. A local supply Authority has supplied a single phase...
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...