Hi all,
Just been to look at a job for a consumer unit changeout, checked the supply and,
Not sure you can see it too well but TNS system with older earthing conductor in green kind of sweated onto intake (connection does not feel too good), but disconnected at the other end (goes into that little 2 terminal connector block).
A BS951 earthing clamp has been put around the incomer and connected in up to the MET on the top left. Ye-hah!
New consumer unit and presumably this, erm, earthing arrangement installed relatively recently in 2009. 25mm tails, 16mm earth, dual rcd etc.
I measured Ze as is and got 0.12 ohms.
Then as an experiment jumped the 16mm main earthing conductor over onto that little 2 terminal block to measure the original Ze - and got 0.41 ohms. Quite a bit of difference, and I suppose might make a couple of circuits non-compliant. There is a bit of insulation stripped from the old green conductor but I can't see how that is relevant?
What to do though?
It's the 2nd example of this I've seen this month, on the first one I contacted my scheme provider and they said that needs sorting first, so I should contact the DNO, but they are under no obligation to supply or repair the earthing. He even mentioned 'earth rod'.
Leave as it?
Reinstate as before the alteration?
Would DNO be interested?
I'd welcome your thoughts - as I say - I keep coming across this.
Cheers.
What to do though?
Leave as it?
Cheers.